Discuss Electric cooker feed SWA external in the Electrical Appliances Forum area at ElectriciansForums.net

yes, and obviously the resistivity of copper/steel is different so using the armouring as cpc aswell as a copper conductor is not advisable
nope.you can use both the armour and a core for cpc. only difference being that if you only earth the armour at the supply end, (to comply with earthing it), it won't be part of the cpc for the circuit.
 
yes, why not? they must be connected to earth the armour anyway. and as for building control. sod 'em on a minor job like this. never seen anyone prosecuted for failing to notify. it's only when someone gets hurt that the suits get off their shiny arses and make noises.
 
At the fault current you will be looking at, the armour and the internal CPC can most likely handle the fault current individually, so connecting them together is really no issue.
 
At the fault current you will be looking at, the armour and the internal CPC can most likely handle the fault current individually, so connecting them together is really no issue.
Not got the idea yet? OP
 

Reply to Electric cooker feed SWA external in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
565
I am installing some driveway lights. The customer wants to be able to switch them on from t he house, but also have a PIR at the driveway...
Replies
12
Views
654
I needs to install 7 external bulkhead lights, but I could do with a steer on bringing the cable into the light - see below The glass which came...
Replies
2
Views
541
For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
652

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock