Hi

Employed electrician to wire extra sockets in bedrooms upstairs in an empty house. However I have noticed when I lifted floor board up to do other work, that the cables are running through holes close to ends of the joists, not within the safe zones, .25 & .4, as with Building Regs.

Looking for advise on how to approach this, with them.

Thanks
Jazz
 
Get back , show regs, ask them to make good (strap joists with extra timber ?) .Dont pay any balance until done.
Thanks will do, was quite shocked when I saw what they had done, at the time so didn’t now about the regs, but it just looked wrong. It was then I checked on the rules about cutting holes in joists.
 
In the old days I always used to drill my holes about 300mm from the wall, did it this way for many many years. Then someone pointed out the .25/4 rule so I now come in roughly .25 the span
 

Reply to Electrician has cut holes to close to joist ends in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
214
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock