He did say for the lid.It is bolted to the left side panel with one end unterminated.
Discuss Full rcbo boards???? in the UK Electrical Forum area at ElectriciansForums.net
He did say for the lid.It is bolted to the left side panel with one end unterminated.
Ah yes didn't read thatHe did say for the lid.
That looks good with the tails all ferruled, i think I will be doing that myselfCut and ferrule for me every time.
Like to leave a little bit length still so the RCBO isn't completely useless if it does need to be moved a little in the future.
View attachment 36659
That looks good with the tails all ferruled, i think I will be doing that myself
Regs don't require ferrules be fitted.
They require the fine stranded wire be protected against damage from the screw terminals which can be satisfied by twisting and then doubling over the strands.
Think the regulation is every connection shall have adequate mechanical strength and be suitable for the terminal or something along those lines
Think the regulation is every connection shall have adequate mechanical strength and be suitable for the terminal or something along those lines