6% below the estimate is well within the range of performance that could be expected from an MCS estimate, the estimates are based on regional data, and within each region there can be +/-10% variation from the average depending if you're in a more hilly rain affected part of the region or the sunniest part.*

Without checking it's hard to know for sure, but I'd suspect that you should be at or above the average slightly where you are though.

I suspect it's probably a combination of most of the factors I've discussed, plus the seagull droppings etc all causing small reductions in output that add up to the reduction you're seeing.

Whether it's worth replacing the inverter or anything else before it dies a natual death is debatable, you'll need to do the maths on something like an £800 cost for a new inverter vs the maybe 3-4% best case performance improvement you're likely to see from it and see whether the figures stack up for you or not.

*this is an issue I've been attempting to sort out with the MCS steering group since the new performance estimation method was put in place, with no success to date.
 
ps it does sound like a proper bodge job, panels should be level, that's just basic level professionalism, and panels that aren't level from one row to another or one panel to another absolutely can cause issues with microshading that some inverters struggle to cope with. There are even threads on here about this from a few years back.
 
showers need a dual pole RCD IIRC.

It's usually simple enough though to wire the circuit to the solar pv from the non-protected side of the RCD.
 
Back from a hiatus of this forum due to it not working with Tapatalk any more.....

Interesting thread, tend to agree with Gavin and Bruce tbh, the performance doesn't seem to be too bad and there are many reasons for why you are under the initial projections provided by your installer.

Does sound like a bit of a shoddy install tbh but not particularly "non-compliant" per sé. My only input at this point would be that the current RCD may be compromised and not able to operate as intended (shower leakage current/earth fault protection) - I would be surprised if there is any "nuisance tripping", and would be more concerned about the trip coil being saturated and unable to trip at all! If the PV is connected on the load side of the RCD, then it needs to be a Type-B variant, as Bruce stated, for this particular inverter.

Btw, 2pole 30mA TypeA RCDs are readily available (as are TypeB) - if the advice about swapping the RCD for a mainswitch, and fitting an RCBO just for the shower is taken on board....
 
Hi,
My advise would be to save your pennies until the inverter dies a natural death and then upgrade to the correct size Inverter with a 10 year warranty which will probably, see the feed in tariff out.
Some people way over complicate things!
 
Hello All,

I'm seeking some advice about a solar PV system we had installed in November 2014 please. After 18 months, we seem to be consistently short of the predicted generation figures. I tried taking it back to the contractor, but they've ceased trading, and it turns out that they never provided our details to the so-called insurance backed guarantee firm. That means we're tucked up a treat, but still paying for the privilege of owning a possibly dodgy system.

They installed a 4kW system comprising 16 off 250W Canadian Solar CS6P-250M panels. The roof pitch is only 22.5 degrees, and we're in southeast England (Hythe, Kent). The array is in a single plane facing WSW, and it's connected to a SunUno TL3KB inverter from SAJ, who've been very helpful so far. They tell me the inverter is rated at 3kW, and that regardless of how much power the panels produce the inverter will cap the output at 3kW. Is it normal practice to install a lower rated inverter than the max power that the panels could produce? Is that likely to be the reason our generation seems lower than we expected? I assume the array can generate more than 3kW on a sunny day. Will that damage the inverter? And perhaps most importantly, is it safe?

The inverter is in the loft, where it's connected to the panel outputs via two isolators. The inverter output is a 2.5mm T&E cable that runs to the airing cupboard, where there's another isolator. That's wired to a 16A MCB which was added into the Shower consumer unit. The shower CU contains a 63A RCCD main switch, and is fed by a 10mm cable from a 50A MBC in the main CU at the other end of the house. There is clear labelling on both CUs. Is that good practice and is it safe? Incidentally, the shower itself is a 10.8kW affair on a 45A MCB in the shower CU.

There are a lot of errors in the inverter log has collected a lot of error messages most of which are grid (codes 02 & 11) or isolation (code 10). While SAJ say they'll help interpret those, is the way the system's connected up a possible contributing factor to these errors? Could it be a function of the array producing too much power for the inverter?

Here's a table with what we've actually generated. The system seems to be working, just not as well as predicted. We're consistently 6% down on the pre-sales estimate. Would an adequately sized inverter correct that?

http://community.NoLinkingToThis/attachments/output-png.13249/

I'm sorry to arrive here as a newbie with all these questions. I know a little about electrics (qualified to the 16th years ago and then never used it...), but nothing about solar. I'm keen to find out as much as I can because there is one glimmer of light; our finance provider says we can make a Section 75 claim to get it put right, if indeed it's wrong.

I'll be really grateful for any advice.

Many thanks in advance

Mark
Thats why I got out if it. Too many cowboys came in and ripped people off, yet MCS who were supposedly there as the installation police did bugger all. Your panels are fine, its your inverter that has not been matched to it. If it was installed at the peak when you couldnt get kit for love or money then chances are they have installed what they could grab hold of. Get in touch with MCS they are supposed to be the ones who oversaw all of this. Who was it registered with Napit or NICEIC? Get onto them too.
 

Reply to Help! Solar Pv System Question in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello, My current 2.5kW Solar pv array is in a less than favourable position, but there is plenty of space to expand the array. I have an...
Replies
2
Views
1K
Greetings, everyone, After dedicating over a month to researching Solar PV systems, I'm nearly ready to make a decision. I owe my progress to...
Replies
1
Views
939
Hello fellow professionals, I'm currently facing a challenging scenario that involves the integration of solar photovoltaic (PV) systems on roofs...
Replies
1
Views
323
  • Article
Electrical2Go - Green2go Launches for All Your Solar, EV Charging and Renewable Needs Green2Go - for All Your Solar, EV Charging and Renewable...
Replies
1
Views
344
Hello Is it possible for solar panel monitoring to over state the actual power generated by the system? My friend’s 6.4kW system has generated...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock