kspray

Ive got the task of sorting out the electrical supply to all the equipment and lighting in our bodyshop as we've just moved to a larger workshop

we have a new board installed with a 125A 3 phase supply installed, the first problem is that the board only has space for 4 circuits

we have the following to supply

electric shutter (10A fuse) 3ph

Spray booth with 2x 4kw fans 9A each 3ph

Compressor (info as on plate on electric motor) 3ph
5.6kW
18.2A/10.6A (might be wrong but im guessing the starting power required is the 18.2A and the continuous draw when running 10.6A??)

Welder 3ph (20A fuse fitted)



what was suggested to me was we should install a single phase board along side the existing one to then run all the single phase items, power points, lighting circuits

first question, the trunking carrying the cables around the shop, its positioned at 2000mm from the floor 50x50 does this have to be metal trunking, or is plastic suitable

who should be contacted to certify the system as safe when the installation is complete

also where will I find the regulations to follow for a commercial property such as ours?

I have done a number of CMS designs for LUL underground stations, but we were talking about huge cable trays with high voltage armoured cables so not really the same thing

finally, best place for me to order the cable, trunking, clips etc..

thanks
 
I assume that there are already circuits in situ?
If so the extra demand doesn't appear to be excessive although we would need to know what's there already
I would have thought that a 3-phase board with 12 or 18 ways would be perfectly acceptable. Why bother with single phase boards when you could balance the single phase loads across the 3-phases at the origin.

IMO Plastic containment system in a workshop would not be suitable. I would look at Galv. trunking.
 
the problem with the board is its brand new, the tight ar*e land lord put in last week and its only 4 way! and from what ive been told new 3ph boards are not cheap

at the moment there is on 13a double socket (wall) in the circuit and a small lighting circuit with approx 6 strip lights and the 3ph 10A roller shutter, all the lighting and power will be removed and redone with our new high bay lighting (single ph) and circuit of strip lights on walls and in the office and machine shop (single ph) and circuit of 13A double gang power points around the whole place and the 4 3ph items listed in the first post

so the thinking behind it was to use the board thats already installed to run the 3ph items and have a seperate dist board for the single ph circuits?
 
You will still need some load balancing of all the single phase circuits.
We are not talking excessive loadings, or size of incomer, or prices within this range
The prices of 125A DBs with Isolator are in the region of ÂŁ200 to ÂŁ300 ( Hager 16W = ÂŁ218). Then breakers, RCBOs, RCDs, switchgear control on top.
You'd probably get the lot for less than ÂŁ3k. A worth while investment if you are manufacturing. Obviously will also depend on the length of the lease.
 
not being nasty mate, but only a fool would 'check and certify' someone else's work and pass it off as their own. sounds like you need a larger TPN db, some 2x2 gAlv trunking, some steel conduit and a competent electrician to install it for you.
 
Ive got the task of sorting out the electrical supply to all the equipment and lighting in our bodyshop as we've just moved to a larger workshop

we have a new board installed with a 125A 3 phase supply installed, the first problem is that the board only has space for 4 circuits

we have the following to supply

electric shutter (10A fuse) 3ph

Spray booth with 2x 4kw fans 9A each 3ph

Compressor (info as on plate on electric motor) 3ph
5.6kW
18.2A/10.6A (might be wrong but im guessing the starting power required is the 18.2A and the continuous draw when running 10.6A??)

Welder 3ph (20A fuse fitted)



what was suggested to me was we should install a single phase board along side the existing one to then run all the single phase items, power points, lighting circuits

first question, the trunking carrying the cables around the shop, its positioned at 2000mm from the floor 50x50 does this have to be metal trunking, or is plastic suitable

who should be contacted to certify the system as safe when the installation is complete

also where will I find the regulations to follow for a commercial property such as ours?

I have done a number of CMS designs for LUL underground stations, but we were talking about huge cable trays with high voltage armoured cables so not really the same thing

finally, best place for me to order the cable, trunking, clips etc..

thanks

Do you already hold nationally recognised qualification in Electrical Installation work?

If you are a qualified sparky then please ignore my comments below, if you are not, then read them several times.

This is a commercial premises, if you are not a fully qualified electrician then working on it is an offence under the Electricity at Work Act, further, being a workplace, do you have someone there with electrical qualifications who can undertake a complete set of RAMS for the job, failure to do this will be a material breach of the Management of Health and Safety at Work Act and the Health and Safety at Work Act. A breach of any of those is a guaranteed prosecution these days. Further, if you are interfering with the supply into the building then you risk prosecution under several other Acts too if your not qualified or authorised to do so.

400V 3 Phase KILLS, it can give you flash burns, set your hair on fire, burn your skin to the bone and cook your organs if you get this wrong. You could burn down your unit if you get this wrong.

Don't be a fool, get someone in who is QUALIFIED, EXPERIENCED AND INSURED TO INSTALL SUCH SYSTEMS INTO YOUR PREMISES. Doing it on the cheap is a fools errand and false economy, if this is a legitimate registered company then the costs are tax deductible, as your accountant will tell you.

Don't risk your life or those of others so save a few pounds.
 
Do you already hold nationally recognised qualification in Electrical Installation work?

If you are a qualified sparky then please ignore my comments below, if you are not, then read them several times.

This is a commercial premises, if you are not a fully qualified electrician then working on it is an offence under the Electricity at Work Act, further, being a workplace, do you have someone there with electrical qualifications who can undertake a complete set of RAMS for the job, failure to do this will be a material breach of the Management of Health and Safety at Work Act and the Health and Safety at Work Act. A breach of any of those is a guaranteed prosecution these days. Further, if you are interfering with the supply into the building then you risk prosecution under several other Acts too if your not qualified or authorised to do so.

400V 3 Phase KILLS, it can give you flash burns, set your hair on fire, burn your skin to the bone and cook your organs if you get this wrong. You could burn down your unit if you get this wrong.

Don't be a fool, get someone in who is QUALIFIED, EXPERIENCED AND INSURED TO INSTALL SUCH SYSTEMS INTO YOUR PREMISES. Doing it on the cheap is a fools errand and false economy, if this is a legitimate registered company then the costs are tax deductible, as your accountant will tell you.

Don't risk your life or those of others so save a few pounds.


read the above and totally agree, ive got a friend who does these installations for a living, I saw him yesterday for him to come and have a look, we will be using him for the install and design, im trying to get as much ready for him as possible, hes not available for a few weeks and we are on a tight schedule so if i can get the trunking installed where hes suggested, and power points in place etc while im having the walls and floor decorated so all he needs to do is run the cabling and set everything up

theres no way i was even contemplating the install, just like to know what to expect and what im dealing with

really appreciate all the replys
 
I hope your friend isn't contemplating using that silly 4 way TP&N board (that the landlord had installed) with an additional single phase DB/CU. As sure as eggs are eggs, a month after it's all been installed, you'll need another 3 phase supply!! Replace that small 3 phase DB and and install a 3 phase DB of suitable size to accommodate the existing 3 phase and single phase requirements, with further capacity for any future 3 phase loads etc....


With vehicle workshops, especially those with spray booths and welders etc, it would be pure folly to install a PVC trunking system as your containment. Keep it an all metal containment system. You'll be far better off all round, for both mechanical and electrical protection....
 

Reply to installing 3ph and single ph wiring into new workshop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
668
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
My dad is knocking down his old out buildings, garage and small workshop, and having a new all in one built with a second storey to be utilised...
Replies
11
Views
4K
Hi all, I've just registered to seek a bit of advice and am sure I'll be looking for lots more help soon. I've just bought a plot of land near...
Replies
1
Views
1K
I work in a location that was once a Machine shop showroom. We have 208/230/480 etc in the building. I need to install a temperature chamber...
Replies
8
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock