Hello and thanks in advance for any replies.

Moved into a new house with garage. My table saw... (https://www.axminstertools.com/axminster-trade-at254lts-table-saw-105573)...is causing the b16 mcb to trip in the small consumer unit in the garage. It is a relatively new saw and don't think it is a short causing the trip but the surge which apparently characteristic of table saws. Garage is powered via a bs5467 armored cable to the main consumer unit in the house, probably atleast 15-20m, with a b40 mcb.

Alot of forums say just to switch out the b's for c's but that sort of general advice sounds a bit too simple! Will that work? Will I need to switch out both mcbs to c type, or will the 40amp in the house cope with the surge ?

Thanks again
Rob
 
The maximum value and type of the MCBs (both the 40A distribution circuit to the garage, and the 16A final circuit in the garage) are determined by several factors - cable ratings, meeting disconnection times, voltage drop.

It might well be acceptable to change the B16 to a C16 in the garage, or it might well not be. Unless you are familiar with measurements like Ze, Zs, and know the cable sizes & electrical lengths, probably safer to say you need to get someone in who is (i.e. an electrician).
 
Alot of forums say just to switch out the b's for c's but that sort of general advice sounds a bit too simple! Will that work? Will I need to switch out both mcbs to c type, or will the 40amp in the house cope with the surge ?
Hi - you are right, it is too simple to be true. The substitution can only be made if the loop impedance is sufficiently low, which can’t be ascertained without a test instrument. Unfortunately the link to the tool didn’t work :(
 

Linked again just for people's reference.

Thanks for the replies. I was hoping a bit of calculation could be done off the back of the details given but I will probably just get someone in. Could do with some more sockets and lighting out there anyway so might aswell get the thing all set up properly. Just have the missus nagging to get other jobs done in the house and need my table saw!haha never a quick fix.
 
I'd try substituting a B20 for the B16 first. There's a Chinese made metal cutting saw that a few of my customers have that suffers from the same problem, and a B20 usually fixes them.
 

Reply to Is a simple switch of b to c type mcbs going to appropriate here? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
The bit where I cut to the chase is in bold below if you can't be bothered with the back story. Changing MCB in main house DB for garage supply...
Replies
9
Views
4K
I've noticed at my grandparents house that all the MCB's in the consumer unit are all type C, every single one of them. Including the ring final...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock