Discuss Landlord Compliance - Query over documents in the The Welcome Forum area at ElectriciansForums.net

Hi,
The only instruction they had was to undertake works to bring the EIRC up to a satisfactory condition.
Thanks
Fiona
I never looks earlier at the consumer unit schedule, it is not clear why they replaced it as the EICR shows no issues with it even the mention of the 16A mcb, as previously stated in #13 is not an issue from the way it is worded. It may be worth asking why it was replaced.
 
Just to add it also says that item 3 incorrect fuse wire has been used but could not see any BS numbers for fuse wire on the report (3036) ,Also agree that no code for the 16 amp MCB on lighting may be just a note) , So that just leaves the cross circuit, easy to fix at the time of inspection . As for The RCD readings I would Guess this is a dual split Load Consumer unit , I would say The EICR was not done correctly,
 
Agreed there is no indication of 3036 fuses on the schedule. The board on the EICR is almost certainly dual rcd, the board on the EIC appear to be rcbos although they are listed as 60898.
This to me is an example of people undertaking tasks they have inadequate competence for.
 
I think the mention of fuse wire may be an autofill from the cert software. Fusewire is used as an example of an incorrectly sized OCPD, not a specific issue.
The wording is exactly the same as it appears in the best practice guide for EICR.
my software also autofills a generic description as soon as I enter a code.
 

Reply to Landlord Compliance - Query over documents in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

My parents had an EICR completed after a change of tenant in the shop and flat property, this took place March 2021. The summary of the report...
Replies
35
Views
5K
I've done a few EICRs for a landlord and the latest one of his I've given an unsatisfactory, I've advised changing the CU - existing one is old...
Replies
18
Views
2K
So I am a fully qualified spark with my own company, however I also have a few properties I rent out. One of my tenants asked if they can have an...
Replies
84
Views
11K
Many will by now have heard of the new requirements for private landlords, enacted under Statutory Instrument 2020 No. 312, known as ‘The...
Replies
48
Views
13K
Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock