Discuss Main bonding Conductor in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
645
Just your thoughts on this one,recently did a bit of work at a factory unit,there are several units being used by a company.
The electrics are really pretty bad,my concern is main bonding of structural metal work,can't really see any Earth conductors to these.
In the one area there are steels for the roof,but are not connected together,this roof got wooden rafters,with the steels holding these & the roof up.
Would these need to be bonded together,which would entail quite a lot of work,these premises have been occupied for a least 20 years,& left like this.
It's really for a visual only report,after the work our company finished,& peace of mind,cheers.
 
If there are roof steels that are just supporting the roof then they will not be extraneous conductive parts because they are not referenced to earth and so will not need bonding.
If they are steel beams bolted to steel uprights that are buried in the ground then they should be bonded, but they would all be connected together by the mounting bolts.
Obviously you could test the metal work for resistance to true earth to see if they need bonding.
 
Thank you,they are referenced to Earth,not too sure they will be connected via roof bolts,will test resistance,off to earn a pound now,have a nice day.
 

Reply to Main bonding Conductor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello fellow professionals, I'm currently facing a challenging scenario that involves the integration of solar photovoltaic (PV) systems on roofs...
Replies
1
Views
289
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
692
Hi all, Figured I'd come straight to the experts with this one because I don't have a great deal of electrical experience. I'm a designer at a...
Replies
21
Views
2K
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hi, I'm new to the site and wanted to seek some advice thanks, relating to adding fused spurs to existing ring mains in a commercial premises...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock