Discuss main Bonding of Water Pipe - supply not unique to property - Potential difference? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

C

Chrishands

Hi, I understand according to 411.3.1.2, that main metalic services incomming must be bonded to MET. but what if the water pipe is shared from another property?
The premises has its own electrical supply, but the incoming water is not individual but shared.
I believe i should still Bond. Could this create any PD between the two properties installations, if they have bonded the pipe also?
 
Re: main Bonding of Water Pipe - supply not unique to property - Potential difference

Yes you should bond each installation if it has it's own electrical supply.

It is the same if you had a block of flats with a service riser feeding each flat and each flat has it's own electric supply.
 
Re: main Bonding of Water Pipe - supply not unique to property - Potential difference

water supply is shared in the street anyway.
 

Reply to main Bonding of Water Pipe - supply not unique to property - Potential difference? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
Apologies if this is in the wrong section - appreciate it's more of an educational question. That said I have 2391 - but the classroom environment...
Replies
2
Views
2K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock