Search the forum,

Discuss Melted socket in the UK Electrical Forum area at ElectriciansForums.net

Jhcp1977

DIY
Reaction score
11
Hi can simeone give me advice I had a electricia install a outside socket that has melted the plug before I ring him can someone tell me if it's been installed correctly? I can't find the makes anywhere online are they inferior products?
I am not happy as my daughter was in the hot tub at the time so shouldn't have something tripped in the house or the RCD on the lazyspa ? As with it all being melted it was still working it's only because she could smell burning I was alerted to it ?
So from what I can see the middle switch is what it's connected to with a single cable running to a outside weatherproof socket any help appreciated
 

Attachments

  • PXL_20210428_073307083.jpg
    249.8 KB · Views: 81
  • PXL_20210428_074112762.jpg
    302.8 KB · Views: 77
obviouslyoverheated, but what's that stuff that looks like chip fat running down the socket?
 
It's just like soot but with it being open all night it's got condensation on it and it's run as for the installation is it correct before I ring the electrician and make a fool of my self or is it just something that sometimes happens
 
Please show some photos of plug and if it has a screwed on top the insides of the plug too. Also a picture of the specification plate of spa or model number.
 
It's just like soot but with it being open all night it's got condensation on it and it's run as for the installation is it correct before I ring the electrician and make a fool of my self or is it just something that sometimes happens
Why was it open all night? that type of outside socket has a lid that can be closed once the appliance has been plugged in, did you in fact do that or was the socket left exposed whilst the spar was in use? The socket could have been splashed with water from the spar, which contain chemicals and compromised the plug.
 
Please show some photos of plug and if it has a screwed on top the insides of the plug too. Also a picture of the specification plate of spa or model number.
Thankyou is this the specification plate ?
 

Attachments

  • PXL_20210428_084328606.jpg
    508.9 KB · Views: 71
  • PXL_20210428_084347789.jpg
    462.9 KB · Views: 69
  • PXL_20210428_084403957.jpg
    239.8 KB · Views: 72
Strange specification, Heating: 2050W, Heating + Bubbles: 1850W I suppose it could cut off one of the heating elements to start the bubble pump, but a bit odd.
 
Hi can simeone give me advice I had a electricia install a outside socket that has melted the plug before I ring him can someone tell me if it's been installed correctly? I can't find the makes anywhere online are they inferior products?
I am not happy as my daughter was in the hot tub at the time so shouldn't have something tripped in the house or the RCD on the lazyspa ? As with it all being melted it was still working it's only because she could smell burning I was alerted to it ?
So from what I can see the middle switch is what it's connected to with a single cable running to a outside weatherproof socket any help appreciated
Looks like the plug top has a loose connection causing the scorching, is the socket leaking? all the, what looks like water marks , I would say it needs a bit of TLC call a Sparky in to sort it out soonest, has the Spa been tested under ISITEE (PAT tested)?
 
Looks like the plug top has a loose connection causing the scorching, is the socket leaking? all the, what looks like water marks , I would say it needs a bit of TLC call a Sparky in to sort it out soonest, has the Spa been tested under ISITEE (PAT tested)?
Yeah going to but my concern is nothing tripped should it have ?
 
Ok thank you but shouldn't have something tripped ?
Unfortunately not, the MCB will only trip on overload, the RCD will trip on leakage faults between lives and earth, the only thing that could trip if you had one would be a AFDD (Arc Fault detection device) these have proved themselves to be somewhat unreliable in the US where they are in use on most installations.
 
Can you post a copy of the electrical installation certificate?
remove or blank the personal details.
 
Yeah going to but my concern is nothing tripped should it have ?
That looks like overheating of the plug, normally the fuse would go if it was all to specification and really overloaded, but often poorer plugs are not able to really do 13A for long periods.

What is the hot tub specification? I.e. is it designed for use with a 13A supply plug & socket.
 
That looks like overheating of the plug, normally the fuse would go if it was all to specification and really overloaded, but often poorer plugs are not able to really do 13A for long periods.

What is the hot tub specification? I.e. is it designed for use with a 13A supply plug & socket.
Does this help ?
 

Attachments

  • PXL_20210428_084403957.jpg
    239.8 KB · Views: 12
that load should be no problem for a 13A plug. as previous posts, I'd say original cause in plug at the fuse. either way, you need a new outside socket.
 
that load should be no problem for a 13A plug. as previous posts, I'd say original cause in plug at the fuse. either way, you need a new outside socket.
Yep got the electrician coming next week can you tell me was she in any danger in the hottub while this was going on as I am in 2 minds to bin it if she was incase it happens again
 
Strange specification, Heating: 2050W, Heating + Bubbles: 1850W I suppose it could cut off one of the heating elements to start the bubble pump, but a bit odd.
I'm wondering if that specification is correct, Heating + Bubbles could be 3900W which would explain the burning plug, but not why the fuse did not blow?
 
no danger in the tub per se. . the only danger would be the outside socket getting hotter and damaging the cable/s feeding it, and any close combustible materials catching fire. get the sparks to fit you a good quality plug while he's there.
 
Why was it open all night? that type of outside socket has a lid that can be closed once the appliance has been plugged in, did you in fact do that or was the socket left exposed whilst the spar was in use? The socket could have been splashed with water from the spar, which contain chemicals and compromised the plug.
No it was left open as I just forgot to close it after switching electric off in the house and unplugging it
 
Thank you all speaking to a different electrician I explained that's there's a single 2.5 twin and earth run straight from a outside socket to a 32amp MCB and he said that's not right any way I will wait and see but what's your opinions on that correct or not
 
Difficult to tell from the picture, but as you say the neutral conductor does look as though it could have been pinched by the top fixing screw as well.
 
Not sure but this is on it
that's a 10mA RCD factory fitted in the tun lead.
as for the 2.5mm cable from a 32A MCB, is that cable direct from the MCB or is it a spur off a socket in the house? if it's spurred off a socket on a ring final, as long as it's the only socket on the spur, it's compliant.
 
Thank you all speaking to a different electrician I explained that's there's a single 2.5 twin and earth run straight from a outside socket to a 32amp MCB and he said that's not right any way I will wait and see but what's your opinions on that correct or not
As long as that cable is supplying only the one double socket outlet, it is technically OK, as the fuses prevent an overload to the cable, though instinctively people would expect to use a 16 or 20A MCB on that circuit.

The issue you had/have is nothing to do with the fixed wiring, and everything to do with the plug and fuse within it.

The fixed installation cannot detect when something connected externally to it gets hot - it could be a toaster (which is OK getting hot), or it could be a loose connection in the plug or poor quality plug/fuse (which would be a problem).

I would suggest either the plug/fuse is not of proper quality, or a connection was loose.

Could you post additional photos of the plug, especially the pins and markings on the pin face?
 
that's a 10mA RCD factory fitted in the tun lead.
as for the 2.5mm cable from a 32A MCB, is that cable direct from the MCB or is it a spur off a socket in the house? if it's spurred off a socket on a ring final, as long as it's the only socket on the spur, it's compliant.
It's 2.5 From outside socket no spurs nothing just that one socket on its own mcb
 
It's 2.5 From outside socket no spurs nothing just that one socket on its own mcb
ideally it should be on a 20A MCB as loads in addition to the tub may be plugged in, so it's not a fixed load. not a big job to swap out.
 
Ask the electrician to fit another plug. Then ask him to measure the current when the spa is in heat mode and then measure current when in heat and bubble mode. You need to confirm that the current is no more than 2050/240 Amps and 1850/240 Amps respectively. Meanwhile I will look up spec and call company. The failure is over current and thence overheating of fuse . This plug socket combination is suitable for no more than constant 10amps because the plastic and rubber construction makes it very difficult to dissipate heat especially generated in the fuse.
 
https://images-eu.ssl-images-amazon.com/images/I/F1cu1b3il5S.pdf

see page 10. The maximum power may well be 2050 + 800 + 50 = 2850 Watts for heater, turbo and pump unless the controller switches off parts of heater when turbo turned on. You need the measurements of current drawn in all the spas modes of operation.

As before a 13Amp plug socket in plastic and rubber with lid of socket closed will fail on overheat if over 10A drawn for more than 30 minutes. The heating effect of the current is a quadratic function ie heat produced is proportional/varies as current x current or current squared. Thus heating effect at 12A is 1.44 times greater than at 10A ie 12 x 12/(10 x 10) - At 13Amps it is 1.69 more than at 10Amps. Typically the fuse and its holder will produce a few watts of heat at rated current which if it is not conducted away will cause considerable increase in material temperature and thence thermal damage as one can see from the photos.
 
Last edited:
I have submitted a technical query on line and will update once I have a response. Meanwhile I have just come off the phone with lazy spa uk support desk who confirm the maximum power consumption of your spa is 2050 Watts so about 8Amps. Time to call the sparks back to measure those currents. If they do not exceed 8Amps or thereabouts then it points to the inadequacy of or fault with the socket plug combo and/or its standard of installation. If more than 10A then I would suspect a fault with spa itself causing excessive over current and overheating as described earlier which you should report and pursue with supplier or lazy spa uk.
 
Last edited:
Studying the plug and a similar one on our kettle ( 2.5kW) in attached photos - the region of most intense heating seems to be along an axis through two points; the middle of the fuse and the rivet joint of the line terminal - upper fuse clip assembly. These two points are both high current density and thus high Joule heating. Permaplugs use bussmann fuses so of good quality. The live plug pins and socket entries show no sign of overheating. Telltale signs to ponder on.
 

Attachments

  • 18505D4F-E289-491A-AE3A-DE96A644630E.jpeg
    304.3 KB · Views: 27
  • D714396F-F199-4003-8C46-5BC62D76F419.jpeg
    302.6 KB · Views: 31
Last edited:
I reckon it would not have been much longer before carbonisation of the plastic former between the plug earth pin and top fuse clip precipitated a line earth tracking current which would be detected by the supply side rcd turning off the power.

My learned EF colleagues may wish to advise the OP on specific questions to ask and confirm with the sparks before he visits since this is an IET special location and installation (GN7 IIRC).
 
Last edited:
You must have had a quiet afternoon, @marconi ? Im sure all the pubs are open now if you're at a loose end
Waiting for the snooker to start......more seriously I have been baby sitting 9 week old jack russell, Maud, with a chronic itchy skin rash - quite upsetting to see her regularly scratch herself, only relieved when asleep or stroked - half way through treatment as advised by vet. Up at 5am because she was so troubled by it. Wife in hospital. was due home Friday but learned for good reason now Tuesday earliest. So needed occupying. Could not go in my man shed to dabble with some electronics ’cos being painted by two fine fellows , father and son, both with Asperger, who to my great shame tested my patience for reasons which are my failure not theirs. So needed distracting. Enough said for somewhat ‘grandstanding’ on this .......
 
Waiting for the snooker to start......more seriously I have been baby sitting 9 week old jack russell, Maud, with a chronic itchy skin rash - quite upsetting to see her regularly scratch herself, only relieved when asleep or stroked - half way through treatment as advised by vet. Up at 5am because she was so troubled by it. Wife in hospital. was due home Friday but learned for good reason now Tuesday earliest. So needed occupying. Could not go in my man shed to dabble with some electronics ’cos being painted by two fine fellows , father and son, both with Asperger, who to my great shame tested my patience for reasons which are my failure not theirs. So needed distracting. Enough said for somewhat ‘grandstanding’ on this .......
It all comes together doesn't it. I hope everything works out well for you. :)
You are a kind man.
 
Waiting for the snooker to start......more seriously I have been baby sitting 9 week old jack russell, Maud, with a chronic itchy skin rash - quite upsetting to see her regularly scratch herself, only relieved when asleep or stroked - half way through treatment as advised by vet. Up at 5am because she was so troubled by it. Wife in hospital. was due home Friday but learned for good reason now Tuesday earliest. So needed occupying. Could not go in my man shed to dabble with some electronics ’cos being painted by two fine fellows , father and son, both with Asperger, who to my great shame tested my patience for reasons which are my failure not theirs. So needed distracting. Enough said for somewhat ‘grandstanding’ on this .......
thank you for taking your time to help me i will show the spark what you wrote as its all over my head hope everything be ok with the dog and wife thank you once again
 

Reply to Melted socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Prima Tumble Dryer which I have had for 5 years. Just recently, the plug and socket melted. I replaced both and it melted again. I...
Replies
18
Views
3K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
716
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Hi all I need some advice and thoughts on what caused this plug on a toastie maker to have given me electrical shock when I pulled it out of the...
Replies
6
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top