Discuss Meter Tails 16mm 0r 25mm in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I was changing meter tails between service head and meter when bloke from elec board came around to read the meter. Had put new tails in between head and meter, then meter to new isolator, but the main fuse was still out. The bloke didn't seem to care. Asked me to put the fuse in for a second in order to read the digital meter, then was quite happy for me to remove it again. Didn't ask at all about broken seals. Maybe i was very lucky.
 
I was changing meter tails between service head and meter when bloke from elec board came around to read the meter. Had put new tails in between head and meter, then meter to new isolator, but the main fuse was still out. The bloke didn't seem to care. Asked me to put the fuse in for a second in order to read the digital meter, then was quite happy for me to remove it again. Didn't ask at all about broken seals. Maybe i was very lucky.


Why would you want to renew/upgrade the supply networks equipment
Better it cost them than you
Also its not very common to do so,they could prosecute you theoretically

Working live has never bothered me,but I would not encourage anybody to do so
We break the law when we do so.but I believe in individual responsibility and being careful whilst confident in carrying it out



Thats my excuse and Im sticking to it:)
 
Peter if you are in any dout as to weather to remove the suppliers cut out. dont be. Basicly the electricity at work act says that every installation has to be provided with a means of isolation for safe working. So if the supllier has provided a means of isolation ie a swich or the meter with a built in isolator (not designed to be switch under load) then all is fine but if they have only provided a cut out and meter then they can not argue why you have cut their seal and removed the fuse. what do they expect you to change the tails LIVE!?????
Hope this helps
Regards
AJ;)


Hi
If you change a fuse board do you have to change the tails.

Thanks

Mark
 
fit a isolator take existing tails and feed into top of isolator and run new 25mm from bottom to db that way if anything needs upgrading its dno side and you havent broke seal and gone inside meter.
 
If you change the CU,you should upgrade the tails to 25mm,only from the meter to the CU.

Hi
But on the advice of the NIC you cannot do this as this would mean breaking the LEB Clip which the NIC say you should not do.

Thanks

Mark

Hi
But on the advice of the NIC you cannot do this as this would mean breaking the LEB Clip which the NIC say you should not do.

Thanks

Mark

Hi
Can anyone tell me the best pace to buy a 17th Edition C/B

Thanks

Mark

fit a isolator take existing tails and feed into top of isolator and run new 25mm from bottom to db that way if anything needs upgrading its dno side and you havent broke seal and gone inside meter.

Hi
But we are defeating the object 16mm to 25mm as long as i upgrade to the same size board the old tails should be fine.

Thanks

Mark
 
Last edited by a moderator:
Hi
But we are defeating the object 16mm to 25mm as long as i upgrade to the same size board the old tails should be fine.

Thanks

Mark
thats not you problem. your tails should be 25mm. dno can upgrade from meter so you dont have to break their seal. easiest option is as described ;)
 

Reply to Meter Tails 16mm 0r 25mm in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
931
Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Replies
11
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
487
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock