So does a main switch.
Isolation was probably the wrong wording. A single pole rcbo may disconnect the circuit as required under certain fault conditions but does not disrupt the neutral which is considered a live conductor, a double pole upstream rcd will.
 
Isolation was probably the wrong wording. A single pole rcbo may disconnect the circuit as required under certain fault conditions but does not disrupt the neutral which is considered a live conductor, a double pole upstream rcd will.
Tin hat on I've never quite got the significance of disconnecting the neutral on a TT. If an RCBO wont disconnect it on a TT it wont on a TN , so whats the difference?>
 
Coming into the discussion a bit late, but isn't 8 megohm a bit on the low side (I relegalise its within acceptable limits) for a two up two down. Wouldn't it be an idea to get that to a higher figure, then dodgy appliances wouldn't have such an impact?

OP did you say you've measured 19 mA? Think most 30mA RCD start tripping at 21, so you've not much scope.
 
Cos I suppose there's a main switch that isolates both Live & Neutral, but I'm no expert here!

I know I've read somewhere about SP RCBO's not being suitable for TT systems but cant remember where and am still sceptical. In fact on our last NICEIC visit I asked the question and got a blank look.
If anyone can shed any light......
 
I know I've read somewhere about SP RCBO's not being suitable for TT systems but cant remember where and am still sceptical. In fact on our last NICEIC visit I asked the question and got a blank look.
If anyone can shed any light......
It is a much discussed grey area. An rcbo is not there to necessarily provide isolation but disconnection in the event of a fault which a single pole device will do. It confuses me and it is not clear anywhere with mixed opinions given.
 
Coming into the discussion a bit late, but isn't 8 megohm a bit on the low side (I relegalise its within acceptable limits) for a two up two down. Wouldn't it be an idea to get that to a higher figure, then dodgy appliances wouldn't have such an impact?

OP did you say you've measured 19 mA? Think most 30mA RCD start tripping at 21, so you've not much scope.
No, it's tripping at 19mA on ramp test with everything on. (23mA disconnected). So there is nornally 4mA leakage.
I realise 8M is a bit low....
Think I'm gonna invest in a leakage clamp meter and have a deeper look - if I get called back that is - still no tripping 48 hrs on......
 
RCBOs with a solid neutral are far from ideal with any earthing system.
If there is a neutral to earth fault then the rcbo will react by disconnecting the line and not actually disconnect the fault.
Thus it appears to the user that a fault has occurred but it is now disconnected because the protective device has operated, when in actual fact the fault is still there.
Plus of course you now have a portion of the neutral current from the entire installation diverting through the fault.

Additionally manufacturers have their own requirements for maximum Zs for correct operation of their single pole RCBOs, which may not be achieveable on a TT system.
 

Reply to Need some ideas - RCD tripping but everything tests fine.... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
791
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
884
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock