Discuss Radial off a ring circuit in the UK Electrical Forum area at ElectriciansForums.net

Gringoking88

-
DIY
Reaction score
50
Hi all,

I have been asked to add a couple of sockets and add power to an existing strip light (currently disconnected) in a garage. There is presently an SWA 2.5 mm cable that is apparently live but taped up, hanging loose in the garage which is fed from a 32a ring circuit located in a utility room. Before you say it yes I know that is madness to leave a live wire like that but it was nothing to do with me (it really wasn't)!

I called the NICEIC just to clarify the RCD situation and was advised to add a garage unit with RCD protection and use two 6amp breakers. My question is why do the breakers have to be limited to 6amps, e.g. I get in effect it would be like having a spur but dont understand why I cant have larger breaker?

Please go easy as I'm just trying to educate myself.

Thanks in advance.
 
firsti'd see if there was a spare way in the house CU, then a better solution would be available.
 
Think NICEIC is the clue to your dilemma, anyway you are down as a trainee yet a DIY post???
 
Andy,

Thats why I asked the question, as I want to understand the full methodology behind their recommendation. I am pretty sure it is a simple answer and probably something I am just overlooking.


Is the supply fed via a FSU? RCD protected? and a bit of advice gain access to the trainee section, you will get more help in there
 
Andy,

Thats why I asked the question, as I want to understand the full methodology behind their recommendation. I am pretty sure it is a simple answer and probably something I am just overlooking.

So, are you a DIYer or an electrician ? I'm still none the wiser.
 

Reply to Radial off a ring circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
302
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, I`m looking for an advice. I have an electric shower that I`m not using due to boiler changed to combi and added shower over bath feed by a...
Replies
1
Views
943
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
904
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock