In a hidden position, a 15A round pin fuseless plug and socket can be fitted on the appliance, with an an FCU above. Then only one fuse to blow.
My suggestion does away with the question of whether to cut off a moulded plug or not.

In reality, no socket behind a kitchen appliance should be made inaccessible.
Couple of screws at most, and even the heaviest of equipment can be moved.

The original question of replacing the plug top fuse with a solid link is of course “no”
 
My suggestion does away with the question of whether to cut off a moulded plug or not.

In reality, no socket behind a kitchen appliance should be made inaccessible.
Couple of screws at most, and even the heaviest of equipment can be moved.

The original question of replacing the plug top fuse with a solid link is of course “no”
Yes, to keep the moulded plug. But a solid link in a moulded plug only gives one fuse on an accessible FCU.
No, the solid links are not available any longer?

If the manufacturer is OK with cutting off the moulded plug, then a 15A round pin is the way to go.
 
I really don't see why you keep pushing this. How many times do your kitchen appliances blow fuses for no reason. If they do it often then I suggest there is something wrong. And if there's something wrong then the appliance is coming out anyway.

And what about using a 20A switch instead of FCU?

Putting a 15A plug on appliances is not a good solution to your 'problem'.
If the manufacturer is fine on cutting off the moulded plug, then a 15A round in an inaccessible location is the way to go, as long as there is an accessible FCU.

Many servicemen are told by the manufacturers that the appliance must be 100% isolated to work on it - that is remove a plug - not trusting that FCU are DP isolation. Hard wire in a fridge and many will not unscrew the appliance cable from the cable outlet then walk away. So a 15A plug is the way.

Also out of the way plugs with fuses can have the plug run hot unbeknown to the user. The heat is invariably around the fuse. A 15A plug with no fuse is safer.
 
Do you know if they are still available or guessing?

Nobody in their right mind would fit one, so I expect not. If you have tried to buy them and cannot, then that proves the point.

I suspect you will still keep asking though. Are you bored again?
 
People here have written that an appliance say under a worktop should have a plug in an adjacent cupboard. Of course a good way. If the accesible cupboard is many cupboards away, with the appliance lead not reaching, then an FCU and 15A socket/plug behind the appliance is the best way around it. Assuming the makers are fine with their moulded plug being removed.
 
People here have written that an appliance say under a worktop should have a plug in an adjacent cupboard. Of course a good way. If the accesible cupboard is many cupboards away, with the appliance lead not reaching, then an FCU and 15A socket/plug behind the appliance is the best way around it. Assuming the makers are fine with their moulded plug being removed.

As long as you're happy, that's all we can hope for.
 
Nobody in their right mind would fit one
Complete nonsense. That is the same as saying "nobody in their right mind would fit 15A fuseless plug behind an appliance."

A solid link converts a 13A plug into a fuseless plug - not difficult to grasp. Guess what? Fuseless plugs are legal. ;)
 
Complete nonsense. That is the same as saying "nobody in their right mind would fit 15A fuseless plug behind an appliance."

A solid link converts a 13A plug into a fuseless plug - not difficult to grasp. Guess what? Fuseless plugs are legal. ;)

I know you just try and get a response from people, so I'll keep biting.

You keep wanting us to answer your question of whether links are available for 13A plugs. After 100+ posts surely even you have realised that nobody on here knows where to buy them. Do you accept that, yes or no?
 
This lot's enough to make the decision 15amp connectors and tape. ?
 
  • Winner
Reactions: DPG
I have not had one yet, as no one knows if the solid links are still available.
I have been in my trade pushing forty years and I have never come across a manufactured solid link for a 13A plug. This obviously does not mean they have never existed but I doubt they have done, why would a manufacturer produce such a thing, how would they certify it as a compatible component for a 13A plug so that it doesn't affect the safety of the original product. A few years back products were being imported, in particular cctv equipment which came with a fitted moulded plug but no fuse, these were flagged up by Trading Standards as non compliant and dangerous.
 
Last edited:
So to bottom line.
  1. No one here has ever come across a solid 13A link, I have, or knows where to buy one.
  2. 15A fuseless plug can be fitted behind an appliance in inaccessible locations as long as an accessible FCU isolator is fitted.
 
Last edited:
  • Disagree
Reactions: UNG
So to bottom line.
  1. No one here has ever come across a solid 13A link, I have, or knows where to buy one.
  2. 15A fuseless plug can be fitted behind an appliance in inaccessible locations as long as an accessible FCU is fitted.

Even I'm bored now ?
 
So to bottom line.
  1. No one here has ever come across a solid 13A link, I have, or knows where to buy one.
  2. 15A fuseless plug can be fitted behind an appliance in inaccessible locations as long as an accessible FCU is fitted.
Several of us will have come across solid links but they were not off the shelf products they would have been home made. There is nothing to say you cannot fit an alternative plug which does not incorporate a fuse however the appliance instructions are likely to suggest, in the UK it should be a 13A plug.
 
I have been in my trade pushing forty years and I have never come across a manufactured solid link for a 13A plug. This obviously does not mean they have never existed but I doubt they have done,
I have come across 13A solid links, and knew guys who used them. Not seen one for years, hence this thread. They may not be available any longer as the demand is not there. Nothing in any reg say they are illegal. Solid links are available for many applications.

The link simple converts a fused 13A plug into a fuseless, eliminating a gfuse -a s do all solid links. Fuseless plugs are legal being for sale - 15A.

A few years back products were being imported in particular cctv equipment which came with a fitted moulded plug but no fuse, these were flagged up by Trading Standards as non compliant and dangerous.
Those are general portable appliances. A heavy fitted appliance is different - some are even hard wired in.
 
Several of us will have come across solid links but they were not off the shelf products they would have been home made. There is nothing to say you cannot fit an alternative plug which does not incorporate a fuse however the appliance instructions are likely to suggest, in the UK it should be a 13A plug.
Some instructions do state various specifics. My oven instructions does not, just connected by a competent electrician and the likes. In the latter there are no problems from the makers when making a guarantee claim.
 
I have come across 13A solid links, and knew guys who used them. Not seen one for years, hence this thread. They may not be available any longer as the demand is not there. Nothing in any reg say they are illegal. Solid links are available for many applications.

The link simple converts a fused 13A plug into a fuseless, eliminating a gfuse -a s do all solid links. Fuseless plugs are legal being for sale - 15A.

Those are general portable appliances. A heavy fitted appliance is different - some are even hard wired in.
Solid links are available for many applications however I doubt you will find one for a plug which incorporates a fuse. If you wish to make your own then go for it there is nothing stopping you.
 
In ye olden dayes, and now, many thought 15A round pin fuseless plugs were illegal (15A round pin fused plugs are available being legal only on radials or spur radials off a final ring). 15A are legal. So they put solid links in 13A plugs in ye olden dayes.

Now we know 15A round pin plugs are legal and great for inaccessible locations, It is awkward manufacturers and their guarantees that are the problem, otherwise just lop off the moulded 13A square pin then fit a 15A round pin.
 
Last edited:
A few years back products were being imported, in particular cctv equipment which came with a fitted moulded plug but no fuse, these were flagged up by Trading Standards as non compliant and dangerous.
Square pin Smart phone charging plugs with the integrated USB plugs do not have fuses. Apple & Samsung.
 
If all this thread is about is cutting off a moulded plug due to warranty issues then there is no requirement to keep the moulded plug for warranty issues, no company can void a warranty simply because you cut off their moulded plug, the only way your warranty can be voided is if it can be demonstrated the replacement plug was the cause of a problem covered by the warranty but that would first have to be proven.
 
If the manufacturer is OK with cutting off the moulded plug, then a 15A round pin is the way to go.
So you cut off the moulded plug and replace it with a non standard plug so preventing it being plugged into an alternative power point for testing by the manufacturers engineer thats an interesting one

I'm sure you must go howling at the moon when it's dark
 
From the current COPISITEE:
16347204765963101452585532448693.jpg
 
It's sort of obvious isn't it that you can't fit brass links ?

Even at 13amp it was never a great system in terms of overload
 
It's sort of obvious isn't it that you can't fit brass links ?

Even at 13amp it was never a great system in terms of overload
The solid links were available. I came to see if anyone had still come across them. I know there is no need for them as 15A fuseless round pin plugs are available. But those manufacturers (mainly from China) again...
 
You can also get fused 15A plugs but the British Standard only permits a maximum 5A fuse, solid link time?
 
  • Funny
Reactions: DPG
You can also get fused 15A plugs but the British Standard only permits a maximum 5A fuse, solid link time?
You can still use BS 546 style round pin fuseless plugs and sockets according to BS7671. These are 2A, 5A and 15A, as long as the socket is shuttered.

15A round pin fuseless plugs are not allowed directly on final ring circuits only square pin 13A fused. See: BS7671. section: 433.1.204.

BS 546, 2A, 5A and 15A are permitted on radials, and that is also a radial spur off a final ring. See: BS7671. section: 553.1.3 Table 55.1.

So you can have a 13A FCU off a Final Ring Circuit, with a 15A fuseless round pin BS 546 say behind a washing machine. Which is the best way to go in such a situation, so the fuse is not inaccessible. And to keep a 13A plug from overheating around the fuse in a continuous 13A current draw.

You can have a 15A mcb with a number of BS 546 15A fuseless plugs on a radial in your home. All legal and above board.
 
Last edited:
Perhaps you might explain the reasoning behind wanting to explore this particular line of thinking, given the infrequent occurrence of blown appliance fuses? It seems as though many respondents, myself included, struggle to comprehend the problem you're seeking to overcome.
 
Perhaps you might explain the reasoning behind wanting to explore this particular line of thinking, given the infrequent occurrence of blown appliance fuses? It seems as though many respondents, myself included, struggle to comprehend the problem you're seeking to overcome.
I recapped that a few times in the thread. People do not read the whole thread just the last couple of posts.
But you might have noticed this in my last post:

"And to keep a 13A plug from overheating around the fuse in a continuous 13A current draw."

This was used on a tumble dryer. Moulded a well. This rarely happens using 15A round pin.

1635000904677.jpeg
 
Last edited:
I recapped that a few times in the thread. People do not read the whole thread just the last couple of posts.
But you might have noticed this in my last post:

"And to keep a 13A plug from overheating around the fuse in a continuous 13A current draw."

This was used on a tumble dryer. Moulded a well. This rarely happens using 15A round pin.

View attachment 91298
That doesn't look like a fuse issue as both pins have suffered thermal damage.
 
All appliances cheap and expensive should be safe. Fixing a superior plug minimises fire risk, if faulty manufacture.
 
Status
Not open for further replies.

Reply to Replacing a 13A plug fuse with solid brass in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening all, I'm upgrading my kitchen electrics replacing the current gas hob for an induction hob. The oven was previously plugged into the...
Replies
6
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Greetings everyone. My first post here, having read a similar thread, I understand that following the manufacturers guidance is all important...
Replies
10
Views
8K
Called to look at a job today for a previous client. Tumble Drier giving off 'funny smell' and tripped the RCD - Called out her appliance...
Replies
20
Views
4K
So I'm based in the UK and I have bought a lava lamp that came with a US plug. After blowing the light bulb (which was also US and was a pain to...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock