Discuss Secondary ccu in the Electricians' Talk area at ElectriciansForums.net

D

Davem

Hi just fitting a secondary ccu to some kennels ad was just think that the secondary board main switch is 60 amps and the breaker supplying from the main board is 40 amp so if there was a problem the main board breaker would trip before the kennel one how do I combat this. New to the game guys please be nice x
 
Ok thank you I thought I could have two stand alone ccu so if there was a problem with kennel ccu it wouldn't trip in the house ??
 
So long as your breakers in the secondary CU are less than 20A then you should have discrimination from the 40A supply breaker, but please do learn what you are installing and what they do, it is very important.
 
So long as your breakers in the secondary CU are less than 20A then you should have discrimination from the 40A supply breaker, but please do learn what you are installing and what they do, it is very important.

You will only have overload discrimination.
As a general rule, MCBs will not offer full discrimination with another MCB, that is overload and short circuit.
 

Reply to Secondary ccu in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
543
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
688
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
854
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
538

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock