Discuss Terminating SWA with Wylex REC Supply Isolators in the UK Electrical Forum area at ElectriciansForums.net

You do not want your calculations running to 100a per unit, drop your shower down to 8kw job and oven to 7kw etc etc. you need to be distributing 60a per unit with 200a per phase 3ph incomer.

if you exceed this the DNO will want you to sell your soul for the cost of the upgrade for your mains. People like tony and E54 will tell you of the frightening costs of big supplies.

It's not that a Ryefield is not ideal for the job it's the fact that you will need 12 sets of tails with 12 main switches all crammed into the trunking with 12 16mm SWA's. with a big DB like this then you still have the SWA glanded onto the trunking but the DB does the fusing, switching and doesn't need all of the tails. You can specify them with a lockable door too.

Btw once you apply cable calcs you may find that you may need 25mm SWA, and on 100a you would with out doubt need it.

I'll work on reducing load, but think 60A is going to be a struggle, 100A is everything on max at once, not made any allowances yet.

I think we're close the the optimum soloution, but to confirm; do you still think Ryefield is the correct soloution, or should I be looking at the Hager invictus TPN DB?

Thanks, really appreciate all the good advice.
 
The hager DB is the cheapest solution by far and would greatly reduce install time, the Ryefield is expensive on the grounds it will also need a hell of a lot of tails and 12 x main switches.

Don't forget when working out max loads you need to apply diversity.

There is no way a bedsit would come even close to 60a let alone 100a, my 4 bed house hasn't ever tipped 50a
 
I agree, it sounds mental. I have a family of 5 with loads of high power stuff and never tripped my 60A. I'll research Hager idea then post my loadings, see what you think.
If I can get down to 60A I can consider T&E again, could I put RCD in Hager?
 
Sorry to say this matey, but with so many questions "up in the air", it does sound like you need the input of somebody with more experience, or you could find yourself in the poop big time.
 
Sorry to say this matey, but with so many questions "up in the air", it does sound like you need the input of somebody with more experience, or you could find yourself in the poop big time.

Sparky got whisked away for surprise holiday, he'll have to have final sign off as its his name on the certificate, but want to get plan ready to discuss on his return as need to crack on.
 
New posts

Reply to Terminating SWA with Wylex REC Supply Isolators in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
889
I haven't seen a lot of discussion on this subject and have questions pertaining to isolation where TN earthing is present and any peculiarites...
Replies
21
Views
739
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
760
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock