Discuss Terminating SWA with Wylex REC Supply Isolators in the UK Electrical Forum area at ElectriciansForums.net

I agree, it sounds mental. I have a family of 5 with loads of high power stuff and never tripped my 60A. I'll research Hager idea then post my loadings, see what you think.
If I can get down to 60A I can consider T&E again, could I put RCD in Hager?

No, T&E submains in flats isnt a good idea, because you then have the issue of discrimination between the sub RCD and the RCD's in the CU. I stand by the 250a DB and SWA being the most cost effective method.

I Echo what Murdoch says, i dont mind helping and giving advice so you know the best course of action to take, a informed customer is never a bad thing. The works proposed isnt particularly difficult and it certainly isnt rocket science, however, it is extremely difficult to do it well!!. and if you do make a cock of it then the kind of total load were talking about normally equates to a big fire.

To summarise: Cut out - Hager 250a DB- 63a sp mcb type c- 6" galv trunking- SWA .........Simples
 
Just had a look at Hager, looks good and probably not much more than original idea. But I don't understand how it works. Plan is to use it as sub main. So main intake to 12 meters, then out of each meter into sub main before going off to each CU.
Hager looks like single 250A in then 12 60A out.
What am I missing ?
 
and to look at some of your earlier threads I would say that you have too much focus on keeping the cost down and not on installing the correct solution.
 
Another ficticuous sparky !

I've tried to ignore your constant nit picking which adds no value to this thread, but your last comment is too much. If you care to research compulsory HMO licensing you will discover it is impossible to get a licence without a certificate.

If you have anything to add to this thread of value please do so, but otherwise please keep your negativity to yourself.
 
I dont remember meters being mentioned, How are you intending on doing this?, it opens a whole can of worms now. are you having your own meters installed and charging your tenants yourself or are you intending on having prepay meters, if its pre pay then the DNN must install them and their own Ryefield to supply them, and that will be big cost!.

If you are having meters in the switch room then you are back to Ryefield - meter - switch fuse - galv - swa and with all of that you will need a switch room the size of a bedsit for all of that 12 x over

if you are having the meters in the bedsits then the hager solution will work. you can get cu's to go in the bedsits that have meters built into them, so it would be
Cutout - hager - swa - cu with integral meter.
 
I dont remember meters being mentioned, How are you intending on doing this?, it opens a whole can of worms now. are you having your own meters installed and charging your tenants yourself or are you intending on having prepay meters, if its pre pay then the DNN must install them and their own Ryefield to supply them, and that will be big cost!.

If you are having meters in the switch room then you are back to Ryefield - meter - switch fuse - galv - swa and with all of that you will need a switch room the size of a bedsit for all of that 12 x over

if you are having the meters in the bedsits then the hager solution will work. you can get cu's to go in the bedsits that have meters built into them, so it would be
Cutout - hager - swa - cu with integral meter.

Brilliant. People think sparking is so, so easy! This is one enormous can of worms
 
his name on test cert your name on design and install ! LOL

No, his name on install, he's got to have the final word. But I will have a big input as you can see. Just to confirm I am not using a one man band but a large company based in Kent with several engineers.
Anyone that has worked with the council knows there is no cutting corners.
 
I've tried to ignore your constant nit picking which adds no value to this thread, but your last comment is too much. If you care to research compulsory HMO licensing you will discover it is impossible to get a licence without a certificate.

If you have anything to add to this thread of value please do so, but otherwise please keep your negativity to yourself.

Its all very well doing research but you've said your sparky (if he exists) is on holiday. Leave it to the sparky to quote you for a price and then if you're not happy get a couple more in to quote.

If you are not happy with the imput from the members here maybe you should try other forums.
 
Brilliant. People think sparking is so, so easy! This is one enormous can of worms

Like i say i dont mind helping with selection of the appropriate equipment best for the application. at the end of the day thats what were here for!, but i stand by my opinion that it would take a half decent spark to make a decent job of it!
 
New posts

Reply to Terminating SWA with Wylex REC Supply Isolators in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
889
I haven't seen a lot of discussion on this subject and have questions pertaining to isolation where TN earthing is present and any peculiarites...
Replies
21
Views
739
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
760
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock