Discuss testing ze on a shared supply cable. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

julianacb

Hi guys I done a quick search but could not find a answer, earthing system in question is TN-S. Supply cable comes in is terminated into two 1361 cut outs and then one set tails then go through to next door into another 1361. Am I wrong in believing that in order to test ze properly the next door property should be isolated and removed from the MET to conduct the test?
 
Hi guys I done a quick search but could not find a answer, earthing system in question is TN-S. Supply cable comes in is terminated into two 1361 cut outs and then one set tails then go through to next door into another 1361. Am I wrong in believing that in order to test ze properly the next door property should be isolated and removed from the MET to conduct the test?

Only the main earthing conductor to the second property needs to be isolated. So you will need to liaise with the neighbour before you disconnect the main earthing conductor to that property. Then proceed as normal to conduct the Ze test in the property you are working in...
There is no need to disconnect the line and neutral to the neighbours property.....
 
Yh fully understand that otherwise the install would have no earth, as for the live conductors they are within sealed holders and never had any intention of taking them out as no need to.
 
To verify that an earth path exists
•Main switch off
•Disconnect earthing conductor from main earthing terminal
•Put one lead on the earthing conductor and the other lead on incoming supply line conductor
•Reconnect earthing conductor to main earthing terminal.
 

Reply to testing ze on a shared supply cable. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
873
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi Just bought this 1960s house, will be doing full rewire. Incoming supply splits and goes through hole in garage to next door. This is a looped...
Replies
25
Views
5K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock