I have a TPN board that will feed 8-10 sub boards. The loads on each board are negligible 5-10 amps peak but mostly 1-2 amps.

The distribution circuits will be fed in 6mm mostly for VD reasons but also to allow some selectivity on the OCPD(MCB) my dilemma is SWA or T&E.

The route is 98% tray before entering a room and feeding a surface mounted consumer unit.

For aesthetic reasons they want the cables in the wall, fair enough, but I'm in a catch 22.

If SWA I'd never be able to gland into the back of the CUs and the SWA would end up surface, if T&E the cable would be in a timber partition but less that 50mm deep thus requiring RCD which completely negates the principle of sub devision of circuits.

1, Am I going OTT worrying about this c0.5m drop from the ceiling to the back of the CU?

2, My "Solution" is to mount a galvanised box above the ceiling, gland the T&E through into some earthed steel flexicon, down inside the wall and into the back of the CU.

3, Am I missing a more obvious simpler solution?

Thanks.
 
I have seen people gland into a through box during 1st fix ( which is often left floating and just pull the single cores through the plaster board wall
 
The "last few cm" of a distribution circuit supply requiring RCD protection is one of the irritations of the regs.
I've long thought that anyone who decides to go drilling in the 20cm above a CU deserves to become an integral part of a new circuit.
Bring back the 16th edition!
 
The "last few cm" of a distribution circuit supply requiring RCD protection is one of the irritations of the regs.
I've long thought that anyone who decides to go drilling in the 20cm above a CU deserves to become an integral part of a new circuit.
Bring back the 16th edition!

If its just the last drop down/up to the CU then it's easy enough to give it mechanical protection. A bit of galv conduit or even a metal plate is all you need.
 
I go out flying kites with the grandkids far more often than I drill holes in the walls of my house.
their is some loose advice out there if you search for it that recommends not to fly kites near overhead power lines. (The sparks amongst us will already know it’s a bad idea)

there are regulations that prohibit running cables an inch below the surface from a consumer unit to the ceiling (230v) where no sane person would drill a hole but a bit of advice not to mess with the 11,000v overhead lines.
over the top maybe?
 

Reply to Thoughts please, SWA vs T&E in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted...
Replies
20
Views
2K
Thought I'd seek some advice on something has been frustrating, and the frustration may now be clouding judgement....! It was 30A rewirable fuse...
Replies
10
Views
2K
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock