but seriously while were roughly on the subject another maybe stupid question from me - how can the minimum recommend size of Earthing conductor for a TT be 2.5mm ?
Basically you are very unlikely to have an earth rod with an Ra below a couple of ohms, more likely tens of ohms, so under fault conditions the maximum current is in the tens to low hundred Ampere range and for a fraction of a second for the breaker to clear it that is OK. Also most TT installations have an incomer RCD that trips at levels of 100mA to 300mA usually.

So basically you won't see a large enough I2t to overload a 2.5mm conductor.

Having said that, personally I would not use anything below 4mm in that case for mechanical strength even for the protected cases.
 
how can the minimum recommend size of Earthing conductor for a TT be 2.5mm ? this is not the main earthing conductor? this is just an out building or something?

Where is this recommendation?

Unless I'm mistaken an earthing conductor is subject to a minimum size of 6mm. And if it is the conductor which connects to the earth rod it is also subject to a minimum size requirement if any part of it is buried.
 
Yeah I might be totally off but OSG 4.4 see table 4.4(iii) for TT "Protected against corrosion and mech damage" 2.5 - also iirc 54.1? BS7671.
[automerge]1592076062[/automerge]
Table 4.4(iii) of the OSG has that for "Protected against corrosion and mechanical damage" cases.

I am not sure I would call it a recommendation though, more of an absolute minimum!
Yeah Can't really see this being adequate but maybe for a car charger or something TT it might be ok.
 
Yeah I might be totally off but OSG 4.4 see table 4.4(iii) for TT "Protected against corrosion and mech damage" 2.5 - also iirc 54.1? BS7671.

That is not a recommendation, that is the minimum permitted.
[automerge]1592076160[/automerge]
Table 4.4(iii) of the OSG has that for "Protected against corrosion and mechanical damage" cases.

I am not sure I would call it a recommendation though, more of an absolute minimum!

Which is my point exactly, it is not a recommendation, merely the minimum permitted.
 
Basically you are very unlikely to have an earth rod with an Ra below a couple of ohms, more likely tens of ohms, so under fault conditions the maximum current is in the tens to low hundred Ampere range and for a fraction of a second for the breaker to clear it that is OK. Also most TT installations have an incomer RCD that trips at levels of 100mA to 300mA usually.

So basically you won't see a large enough I2t to overload a 2.5mm conductor.

Having said that, personally I would not use anything below 4mm in that case for mechanical strength even for the protected cases.


So what if metal water piping or CATV gets added latter lowering the fault loop path?
 

Reply to Twin and Earth CPC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
Good evening all, Some help with following would be much appreciated. A 20 Amp rcbo in a CU supplies an adaptable box on the outside wall of a...
Replies
17
Views
16K
My assessor said that the minimum CSA for a Main earthing conductor for a TT was 16mm. I questioned this as I thought it was 4mm. Regulation...
Replies
30
Views
11K
Hi all, first post, and it relates to quite a challenging installation. The short version is that I'm working through remedial work on a 75 page...
Replies
13
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock