I love that video, but I will still call BS on that third contactor 'till the day I die. I've watched it a number of times and the contactor certainly doesn't appear to move at all.
I'll have to watch it again. I love your avi btw!
Discuss Twin and Earth CPC in the UK Electrical Forum area at ElectriciansForums.net
I love that video, but I will still call BS on that third contactor 'till the day I die. I've watched it a number of times and the contactor certainly doesn't appear to move at all.
Basically you are very unlikely to have an earth rod with an Ra below a couple of ohms, more likely tens of ohms, so under fault conditions the maximum current is in the tens to low hundred Ampere range and for a fraction of a second for the breaker to clear it that is OK. Also most TT installations have an incomer RCD that trips at levels of 100mA to 300mA usually.but seriously while were roughly on the subject another maybe stupid question from me - how can the minimum recommend size of Earthing conductor for a TT be 2.5mm ?
how can the minimum recommend size of Earthing conductor for a TT be 2.5mm ? this is not the main earthing conductor? this is just an out building or something?
Table 4.4(iii) of the OSG has that for "Protected against corrosion and mechanical damage" cases.Where is this recommendation?
Yeah Can't really see this being adequate but maybe for a car charger or something TT it might be ok.Table 4.4(iii) of the OSG has that for "Protected against corrosion and mechanical damage" cases.
I am not sure I would call it a recommendation though, more of an absolute minimum!
Yeah I might be totally off but OSG 4.4 see table 4.4(iii) for TT "Protected against corrosion and mech damage" 2.5 - also iirc 54.1? BS7671.
Table 4.4(iii) of the OSG has that for "Protected against corrosion and mechanical damage" cases.
I am not sure I would call it a recommendation though, more of an absolute minimum!
Basically you are very unlikely to have an earth rod with an Ra below a couple of ohms, more likely tens of ohms, so under fault conditions the maximum current is in the tens to low hundred Ampere range and for a fraction of a second for the breaker to clear it that is OK. Also most TT installations have an incomer RCD that trips at levels of 100mA to 300mA usually.
So basically you won't see a large enough I2t to overload a 2.5mm conductor.
Having said that, personally I would not use anything below 4mm in that case for mechanical strength even for the protected cases.
So what if metal water piping or CATV gets added latter lowering the fault loop path?
So what if metal water piping or CATV gets added latter lowering the fault loop path?
Cable TVWhat is CATV?
Reply to Twin and Earth CPC in the UK Electrical Forum area at ElectriciansForums.net