do the transformers have to be de energised to change taps or do they bang it live ?

its done live.

Switched live they will go bang, don’t even think about it.

On load tap changers are normally at the 33/11KV transformers.

Off load
TapChanger-1.jpg


On load
Tap-Change-4_zpsc9e20d66.gif
 
Switched live they will go bang, don’t even think about it.

On load tap changers are normally at the 33/11KV transformers.

nice animated diagram.

recently read a HSE report that was linked on the IET forum that reported on the death of a sub station worker that was killed changing the taps manually - the mechanism connected to the operating handle failed , jammed between 2 of the contact points , chamber overheated , explosion with hot oil ensued with no warning - terrible way to go , DNO's subsequently changed their proceedures etc.
your 2nd pic is exactly the same as the technical video shown by the HSE
 
Last edited by a moderator:
nice animated diagram.

recently read a HSE report that was linked on the IET forum that reported on the death of a sub station worker that was killed changing the taps manually - the mechanism connected to the operating handle failed , jammed between 2 of the contact points , chamber overheated , explosion with hot oil ensued with no warning - terrible way to go , DNO's subsequently changed their proceedures etc.
your 2nd pic is exactly the same as the technical video shown by the HSE

That was terrible and I feel so sorry for the guy’s family.

There was a known fault on the tap changer and he operated it live.

Operating a tap changer isn’t a nice experience, the transformer sounds like its being violently sick.
It would be very rare you did it using manual control, they are normally under the control of a automatic voltage regulator.
If you watch the animation there are times where there are shorted windings which is where the two reactors (inductors) come in to play. They limit the current in the shorted windings.
 
Im pretty sure that the minimum is 216V for tolerances allowable if l remember correctly. Please put me right if im talking piggie-excrement. I think its nominal voltage 230 -6%=13.8V which is 216.2V to +10%=23V which is 253V...
I ask this question to the DNO just the other day and that's the answer they gave me too, The customer had a load of them GU10 compact florescent lamps that were only lasting a few months (the voltage was around 149 volts at the lamps and 151 at the incomer) The lamp supplier said that due to the higher voltage the lamps could be over heating ,mind you they are discontinuing these lamps so suggested fitting LED lamps instead.
 
Nominal voltage 230v permitted tolerance +10% / -6% 216.2 v - 253.0 v (bs7671, appendix 2, section 14).

Volt drop- 3% for lighting circuits, 5% for other circuits.

Probably repeated what others have said earlier..so apologise if so.
 

Reply to volt drop calcs and 230 v in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
940
Hi! I’d like to install a pedestal-mounted (230 V, 30 A max - programmable) EV charger close to my driveway, which ends about 12 feet away from...
Replies
1
Views
4K
Hi all, I am currently doing my 2391-52 and have been given a mock paper, one of the questions is around vold drop as per below, can someone...
Replies
20
Views
5K
Select (Scottish) Certification Scheme Question on volt drop from 2391
Hi all, I have worked out the volt drop on other questions using the formula mVxAxM. had no issues, but this question below has just fried whats...
Replies
26
Views
6K
Hi folks I am retired and only tend to read the weekly summaries. I read the long-winded thread re. the storage heater and MCB tripping (thread...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock