Kurtis the point is though it is the RCD itself that you are testing.
 
Its states the load should be disconnected from the test, basically disconnect anything from sockets ect,
As thats the load, now theres nothing using current (load) it doesn't state it has to be done at the rcd, it actually states between the line conductor of the protected circuit and the associates cpc. Which can mean it can be done on a socket
9a3e82a0dbf05d56a21af91bb1ddff01.jpg
 
Mate, several pretty well respected people on here have told you the correct way to carry out this test. GN3 tells you how to do the test. The MIs will tell you how to do the test.
Why are you clinging to your incorrect method?
 
The load side of the Rcd for me are the terminals at the bottom of the Rcd
 
I still see that as any load items, not the circuit itself.
My reasoning:
The order of tests as per GN3, dead tests, live tests, with the last test being the RCD test, not test the RCD then connect the circuit and test the circuit.
If you were to disconnect the circuit to test the RCD you would then in theory need to then do the other live tests again to ensure your connections.
The RCD is designed to protect a person from a shock with the circuit connected.
 
I did t say there wrong, theres more methods to alot of testing rather than just one, Im not saying my ways better im just saying if you simple go and replace sockets you don't want to take the board apart unnessessily, though a zs test and rcd test can be done saftley and quickly
 
Last edited by a moderator:

Reply to Whats this mean on a rcd test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
377
Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
422
Hello. I will be buying new apartment to live. But electrical plugs are older. Not the newest. And my question. It will be fine to plug pc in this...
Replies
4
Views
419
Hi, I was looking at my dishwasher and it has this metal plate with these markings. I am confused about the meaning of "10/16A" - does that...
Replies
4
Views
249
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
855

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock