o.k. bs 1361 fuses have earth fault loop impedance times as follows
80A-0.40ohms
100A-0.29ohms
(yes based on 80% values, 5 secs distribution)
In a TNS you can goto a max 0.8ohms Ze
so even if you use the smallest rated fuse in your service head, 60A still max only 0.56ohms and your Ze was...
As title says I've got 3 60a and 10 30a bill fuses to sell any offers please private message will post out payment via PayPal unless collecting thank you for looking
Jonesy83
Thread
30amp
amp
available
fuse
fuses
porcelain
rewire
still
these
Evening all...just a quick question. A customer was using a wallpaper stripper on a ring circuit, smoke started coming out of the back of the socket before the 32amp breaker tripped, what I don't understand is why the 13amp fuse in the plug didn't break? Could someone tell me why? Thanks
Undertaking an eicr on a small commercial unit, tpn 100a 1361 main fuses to tpn dist board, 16mm tails
i have only read the side of the fuse carriers not actually pulled the fuses to confirm
i have clamp metered the supply at a roughly peak time in the premises and had <30A across any one...
Im preparing a house Ive rewired for an niceic assesment. The supply requires upgrading from 60 to 80amp. Ive dpoken to the distributing comany who say it can be done. Should I get my supplier ti do this or can i do it myself. Would thry also reconect the tails for me to the new Cu. Im guessing...
If a domestic installation has 16mm tails from the consumer unit,lets say old 6way with 60amp double pole switch, and cut out 25mm tails100amp,customer does not want to upgrade fuse board and tails.do you think the dno would downgrade cut out?
Recently more than once in PE and even on here I've heard about sparks finding red main fuse carriers with only an aluminium tube inside, and not the expected fuse.
now i come from an electricity company background, but never came across this in the 11 years I worked in that part of the...
I recently asked my electrician to add 4 new sockets to my kitchen, following a re-arrangement of my kitchen appliances. These supply a kettle, toaster, microwave, George foreman and a fridge. The issue he had was there was no ring main in a convenient place, only a spur to a single socket...
Hi,
I work at a local council and our NIC assesment has brought up the age old problem. I know what should be done and what i have done thousands of times in the past, but some of our operatives are being funny about it.
They are refusing to pull fuses as its "ILLEGAL"
I want to put out a...
benieb
Thread
again
council
cutting
fuse
fuses
local
pulling
really
seals
sorry
start
Hi all
Which fuse am I most likely to come across on a domestic property cut out fuse 1361 or 88
I understand that an 88 comes with bolt holes or clips and 1361 is a bigger version of a 1362 fuse
Hello all, hoping someone here can help me out with something that is really getting under my skin.
As part of some work ive done for a regular customer, I have installed 5 new smoke detectors to his existing system (he wants mto turn a big flat into bedsits). Now, I have limited experience...
BS7671 tables only go to certain size fuses eg how can I find max ZS of 400 amp BS88 - 2 on niceic test sheets they ask for a max value out of regs table I have only managed to find a busman fuse chart which differs been told by employer to use these values on sheets any input would help thanks
BS7671 tables only go to certain size fuses eg how can I find max ZS of 400 amp BS88 - 2 on niceic test sheets they ask for a max value out of regs table I have only managed to find a busman fuse chart which differs been told by employer to use these values on sheets any input would help thanks
hello everyone.
i need help here
im now create kind of model of substation for my project .the device and component already given which is put in the panel.
now im hope everyone can help me to check whether my single line diagram are correct?
sorry the image
Hello I was told the other day that they used silver in the old BS88 fuses but he wasn't sure when they got phased out, can anyone shed light on this please if it true or not ?
Following on from a recent thread. My head started to hurt after someone posted (and I can't find the thread now, so I'll just have to quote what I copied, credits to whoever wrote this.).
Being a Electrical Trainee I couldn't quite get me head around that so, as a picture is worth a thousand words, I drew it...
Hi all,
I commissioned the renewal of some mains intake equipment at a building that involved a full shut down. The building runs 24/7 and so a shut down is a VERY rare event. Upon completion of the works the contractor informed me that the 95mm 4 core cable feeding the building was being...
markc17
Thread
amp
building
buildings
cable
ducting
fuse
fuses
under
Hi,
I have old style Wylex push button breakers at CU, and these are labelled as BS 3871, Type B and are 5 & 30 amps. I can not find any ZS values in the regs for these, but see these labelled as N/A. Any help apprecriated.
Thanks
Ken77
Thread
button
fuse
fuses
nominal
these
type b
values
voltage
wylex
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.