  1. VoltzElectrical

    why the light doesn't work!

    I was fault finding a streetlighting column today and found this. That'll be why the light doesn't work then. Wouldn't it have been better to drop a new length of cable in instead of using chokky blocks? They have their place sure, just not inside the very top of an exposed lighting column.
  2. N

    Tails greater than 3m length..

    Hi all, I know tails are meant to be less than 3 metres in length and if not then a switch fuse needs to be installed. What's the situation when the tails from a flat go from a communal hallway then into the consumer unit? (Approx 5m) Do you just put a switch fuse next to the meter? (The run...
  3. H

    maximum meter tail length and composition

    In order to meet current regulation the maximum meter tail length should be no more than 3M and if over a 100amp fused switch should be fitted - is that correct. (This guidline is not in the iet on-site guide except that this maybe specified by the distributor) 521.10.1 mentions that the tails...
  4. S

    Length of meter tails

    Been asked to quote a job - total rewire of four flats. As individual flats it's all very straight forward, ring, lighting, shower etc. However UK Power networks are installing a new head and meters for the whole block on the ground floor. Obviously the distance to the top flat is going to be...
  5. B

    max main bond length

    Hello people Doing cu change , TNCS, upgrading bonding , the gas is other side of house , cu in double garage had to take cable up into bedroom above in trunking and then across loft down external wall i conduit into gas meter box and bond there. When measured route it came to abouty 25m but...
  6. M

    Length of DC cable run

    Hi guys. When using a DC volt drop calculator, when it comes to the length of DC cable run,does that refer to the distance of the panels from the inverter or the distance of the cable from the - terminal of the inverter to the positive. As in the length of the single core circuit from positive...
  7. telectrix

    RCD or NOT

    Situation is: customer has installed a 6mm cable to his shed for a couple of sockets and a couple of lights. he has actually made a very good job of it, 6mm T/E in 20mm pvc conduit, all surface ( none buried.). now he wants me to supply accessories, MCBs etc. and connect up. as it's outside, i'm...
  8. B

    Immersion length

    What is the standard length of the heating element within an immersion tank? Need to replace one tomorrow and would like to know if they are standard size before I go to job The tank has one element only, located at top of tank
  9. P

    Extension Lead maximum length

    Sure I am missing something obvious here but having recently gotten into PAT I am confused by some of the extra long extension reels available. The code of practice for in service inspection & test states clearly the maximum allowable length of extension leads in relations to csa of the core...
  10. K

    Voltage droop

    Hi guys and girls I'm new to the forum and it's probably on here somewhere but could someone please tell me a simple way of calculating volt drop as I'm not having much joy with the Maths side of things and I've got my 2391-10 in two weeks as easy as possible plse
  11. C

    Consumer unit length from main cut out

    Hi , I doubt there will be a regulation against it but is there a maximum distance in a domestic property between the cut out and meter and the fuse board for the flat? Currently in a flat iv been at there is a redundant storage heater board beside the meter and main cut out which will be ripped...
  12. L

    Length of cables

    Just changed an FCU, and terminals are in different places, therefore a bit tight for some wires. Just wondering what length of cable you all leave in back boxes for such eventuallities! Cheers
  13. S

    Radials Circuit Designing

    Hi guys, doing a rewire in which i plan to do the circuits in 4mm as radials, one down one up and kitchen. When designing how can i work out the loading along the circuit? Also how can you work out the loading on a lighting circuit radial as the load will be split along the length so the...
  14. B

    Distribution of load on a ring final for Voltage drop calcs?

    Just pondering my voltage drop calcs for a fused spur off a ring final. Additional circuit will be around 15-20m long so I though I should do this properly.... My problem is calculating the voltage drop in the existing ring to the point of the spur which of course depends on distribution of...
  15. J

    Tt earthing conductor max length

    Hi All, Is there a maximum length for an earthing conductor, which is connected to the earthrod in a TT installation? If so, does anybody know what the max length please?
  16. S

    rcbo fly leads

    quick question can u cut the neutral and earth fly leads of a rcbo when installing them into a distibuton board so you can make them look somthing? the curly neutral lead is a pain i want to straghten it and cut it to fit is this allowed?:banghead:
  17. F

    Continuity Testing

    Testing a lighting circuit with a long lead, all readings R1 R2 Rn around 0.6 to.08 ohms. Adding R1 + R2 = more than 1 ohm. Is this acceptable for recording as the result or should it be less than 1 ohm. TT system. Thanks for any advice
  18. S

    Feeding a out building 77mtrs

    Hi All, Am installing a ring circuit of 5 sockets,10 x 5ft twin flourescents & 6 x 400w pir flood lights into a outbuilding used for storage. I am thinking a 10mm 3 core swa will be suitable. The run is 77mtrs. Am going to stick a 40amp RCBO at main fuseboard and a rcd board in...
  19. D

    Surge protector cable length (quick question)

    Hello all. I'm hoping someone can answer this (probably simple) question I have... I just bought a surge protector mini extention cable to keep with my laptop. It comes with a moulded 2 meter cable, standard UK plug on the end of it, and on the bottom of the unit, the words: NON REWIREABLE...
  20. E

    ring design and voltage drop

    Hi guys. Ive generally no problem going through the deign process of cable selection for a circuit to be installed, (i try keep my hand in now and then rather than just looking in the OSG) but when i look at a RFC as in appendix 15, i get a little stuck. Ib = 32A, so In = 32A breaker, take it...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock