Hi all what is the maximun length of a ring main in 2.5 te can you install as doing an extension in a bungaloe and the board is the other side of the building we going to be protecting the circuit with a 20amp mcb no larage loads as it feeds bedroom and lounges there will be no insulation on the...
I've yet to come across this problem but like every good scout I like to be prepared.
If a circuit is over the maximum volt drop permitted but fixed in the length of the circuit, how would you over come this? Would it be a simple case of using cable with bigger csa? Does anyone else know of...
Here's the problem.
We have a self regulating trace heating tape installed on a piping process line where we need to know the length of the tape.
The tape was estimated to be 10 metres (approx 32.8 feet).
However the guys who installed it have reported that they have installed 19 metres...
xwhitemousex
Thread
aus
cable
heating
help
length
measure
metres
self
trace
hi all is there a regulation for a single phase board in a domestic property which is going to supply (from mains) a seperate sub board for an additional installation.ie a garage,
is there a minimum requirement for size and length of new mains cable supplying the new sub board,also does having a...
bobby101
Thread
aus
board
cable
check
garage
length
main
mains
max
phase
property
single
single phase
supplying
I have just recently started a new job-its a nursing home and I have been giving the work of 1st & 2nd fix to the 60 odd ensuite rooms.The job is on 2 floors and there is only one dist board on each floor.I have been instructed by the foreman to wire one ring(and one lighting circuit) to do a...
Anybody had any problems using a Schuco fixing brackets with curved clay tiles?
Also, does it matter whether you use the pos or neg for the long cable back to the isolator?
Evening all
Hopeully someone can help me get my head around this.
I'm looking at table 7.1 OSG. For the 1361/3036 45A radials on a TN-S system the limiting factor is sc, which means its limited by the line to neutral loop impedance (short circuit). But the TNC-S it isn't. Can't see what the...
Has anyone ever had to replace an underfloor heating temperature probe?
I know there supposed to last but if one ever did fail I can't see how it can be replaced, it comes with a length of flexible conduit, easy enough to pull the old one out, but would be a nightmare slide a new one in...
TPES
Thread
aus
conduit
heating
length
probe
replacing
underfloor
underfloor heating
Hello,
Relating to a house/domestic installation, is there a maximum length for 25mm meter tails? I have got it into my head (old age creeping in!) that it is a metre - need confirmation/advice about this from any kind souls watching. Thank you, from member's first posting.:o
VOLTAGE DROP CALCULATION FORMAT
hi my friends,
is anybody have voltage drop calculation format?
AND THERE BEEN SOME CHANGING OF OPINIONS AND ADVICES AS FOLLOW
1ST REPLY
Shabu there's a few ways of calculating volt drop, the vast majority provide you with an "average" assuming the load is...
ecservices
Thread
cable
calculation
length
reply
sorry
voltage
voltage drop
volts
can someone please help me with this question
There is a 40A BS88 fuse, protecting a 10mm cable with a 4mm Earth, it is wired to Reference method C, supply is TNS and it is protected by a 30mA RCD. What is the maximum length the cable can be?
(thats all the info i have! I haven't been to...
can someone please help me with this question
There is a 40A BS88 fuse, protecting a 10mm cable with a 4mm Earth, it is wired to Reference method C, supply is TNS and it is protected by a 30mA RCD. What is the maximum length the cable can be?
(thats all the info i have! I haven't been to...
We are all familiar with the requirements for measuring Zs and verifying that it is within the limits for the particular type of protective device. I use a single guide of 1.2 ohms as the maximum though there are of course many variations.
What we (I) have not been noting is (R1+ Rn) and the...
hey guys i am studying for my C&G level 3 and i have my practical inspection and testing next week and i cant find anywhere thae values that are aceptable when you read continuity on a lighting circuit for instances and they havent told us at college
i presume it is somethning to do with the...
A 1.5mm2 conductor has a design current of 4 a and a length of 10 meters. its volt drop is 29 mv/A/m what is the volt drop across the terminals.
Can anyone show me how to work this nasty little bugger out
Answers are
11.6v
17.4 v
1.16v
1.74 v
lofty84
Thread
answer
aus
because
electrical work
length
metre
out
volts
work
i recently had to add a spur from a ring to supply a item of fixed equipment. I took the supply from a socket into to a switched fused spur and placed the necessary fuse for the equipment directly after the socket then a 10 meter cable run to a flex outlet connection unit then a 0.5m flex cord...
scott.rick
Thread
aus
cable
equipment
fuse
fused
fused spur
isolation
length
means
spur
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.