seperate

  1. M

    PV tripping another RCD on seperate circuit?

    We have installed a PV system which has 3 inverters and is protected by a 300mA RCCB. It runs directly back to the main incomer. However there's another circuit which runs from the same point which is protected by a 100mA rcd which is tripping. The 100mA RCD feeds a distribution board which...
  2. T

    Running Seperate CPC to light fitting HELP PLEASE

    Hi Guys A customer wants to replace a class 2 fitting with a class 1 the lighting circuit does not have a CPC, I want to run a seperate 1.5mm CPC but as its less than 4mm does it need mechanical protection? And is it acceptable to only run it to the fitting in question? Your help with this...
  3. I

    seperate bonding conductor

    hi when running a 10mm bonding( seperate to the cpc proctected distribution circuit) conductor for a pme supply to a detached garage that contains (water/gas services) is it ok to run from exisitng house cu to gargae cu and then bond the services to garage cu. or does the bonding conductor have...
  4. oxford 12

    rcd tripping

    Just been called to a tripping problem in a lab,where 3 seperate rcds would trip out for no reason.After some time discovered a heat damaged neutral connection in a seperate db in another part of the building.With this connection repaired ,the tripping problem ceased.Can any one explain this...
  5. B

    eicr and test help

    hi all i would like some advice if possible, i came across a situation that is annoying me, a small retail outlet a tp&n db fed of 15mtr run of swa which is controlled via a seperate isolator at cable head 1: the db didnt have a, frying pan or a seperate earth from swa to the met, which i...
  6. C

    2 way light connected to 2 different circuits

    Hi I have just carried out a CU change and when I tried to replace the lamp in the fitting on the landing It keeps throwing the breaker. The fitting is 2 way and connected to both the upstairs and downstairs circuit. I haven't come across this method before, so it confused me a bit. How dies...
  7. B

    2 circuits

    High today at a fault call i noticed that on a row of lights that were out the swa that fed them was also feeding the other row so two seperate circuits fed via 2 seperate mcbs eg lives, neutrals+ cpcs all in the same multicore armoured i informed the client this would need rewiring with a new...
  8. H

    multiple cores for same circuit?

    some plonker ordered and installed the wrong swa cable (too many cores not enough csa) but honestly the csa issue is only due to voltage drop. So I was wondering your opinions on using multiple cores together as parallel conductors? I've looked at the regs and it looks okay but I may have missed...
  9. M

    Lighting Dimmer Switch with seperate switch

    Can any one tell me of a manufacturer that still makes a lighting dimmer switch with a seperate on/off switch? To make up with grid components works out quite expensive. This is a request from a client who doesn't like the standard dimmer switch. Many thanks in advance for your replies.
  10. E

    Wiring combi with seperate programmer and thermostat

    Hi all, First bit of heating controls that I have done apart from wireless, so please bear with me. Plumber friend has fitted boiler Worcester Greenstar Junior 24, wants it wired up, RCD protected fused spur already in place (from old boiler) he has given me a Horstmann ChannelPlus XL...
  11. S

    3 phase supply + 3 seperate ground mounted systems = 3 systems (3 FiTs)

    We have a customer that wants three seperate ground mounted systems. It is a farm which has a three phase supply with each phase supplying a seperate dwelling. With it being a farm the it is only on one set of deeds. The set up is that the father lives in the main farm house with his sons...
  12. A

    Is it allowable for a shop to run off two meters which is two seperate supplies

    The shop in question was two seperate units which has been converted into one unit years ago. The business uses both the meters for the electicity supply is this allowable or are they supose to run on one meter only? This would release a meter and supply which would be beneficial for the flat...
  13. D

    Seperate EICs

    Hi guys, If in a house you changed a consumer unit and fitted 3 new circuits. would you use 1 eic or seperate eics for each circuit? I keep getting conflicting views Thanks
  14. T

    Can you buy wylex busbar seperate from unit?

    Bloody apprentise cut the busbar to short to go to main switch, Only reaches 83A rcd and 5 MCBs. Anyine know were i can buy a new one from if possible??
  15. N

    Help Power One Aurora / Sanyo HDE RCD tripping

    Odd one. Installed a system last Thursday. all tested. All good. Went back to adjust panels and as soon as we reconnected the RCD tripped... and continued to (and stand-alone). Seemed to trip as we approached 2kw (of 3.8) but might have been coincidence. Checked the IR for the cable run...
  16. SolarCity

    Dual MPP tracker inverter - two different panels?

    My colleague asked me earlier if it was possible to fit different panels to an inverter that had a two MPP trackers - for example a string of 10 Sharp 185s on one MPP tracker and another string of 7 Sharp 245s on another? I didn't know so I thought I'd ask on a forum where someone probably does.
  17. Golden_Boy

    Seperate Circuit For Fridge/freezer !!

    After returning from Greece after a two week break I found my Kitchen RCBO had tripped.:icon9: However as I had the forsight to provide a dedicated circuit for the freezer all is well.:) Why dont folk heed the advice and do this when having a rewire as a matter of course?
  18. N

    Existing Spur -> 2 x Seperate outlets.

    Hi all, Considering mounting my T.V on the wall in my bedroom and as I'm decorating I thought I might as well put a few more sockets in instead of having extension leads on the floor and wires hanging down the wall. My question is this. I opened up the socket that is there and what I thought...
  19. jibjob

    Multiple wires in MCB, what's the best way to record on PIR?

    Anyone have any advice on entering test results for multiple wires from the same MCB. It's a 32a MCB with a ring final and a further 3 wires stuffed into it, all of them radials. I'm not sure of the best way to express this on the cert without it looking a bit cluttered and probably all the more...
  20. D

    3 phase Meter Arrangement

    Hi, I have been asked to 'get the installation ready' for the electricity supplier to come and fit seperate meters. Currently:- The building is broken up into 5 seperate dwellings There is a 3 phase supply running straight up through a Ryefield dist board. The 3 phase and N Supply cable has...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock