Discuss 6 cables in a backbox? in the UK Electrical Forum area at ElectriciansForums.net

D

Deleted member 112675

Hello Everyone

Will be wanting a grid switch with 4xdp switches to control 4 spurs with a single socket on each. Ring main in and out plus 4 spurs of the switches equals 6 2.5mm cables. I've got a 4 module mk grid backbox - about 45mm depth I think.

Is it possible? I'm thinking the 4 spurs might just enter the bottom of the box and go straight into their respective switches but it might be hard to get all 6 earths terminated?
 
47mm back box and:

2273-208.jpg
 
Beginning of the summer tested ten houses for a housing association on a five year old estate. Eight out of the ten had open continuity faults on at least one conductor on the kitchen ring final circuit. Back to do remedials, first house found in 30 odd minutes at the four gang control grid. All bar one of the others at the same point. Half a day I had resolved all eight. Bad design? or the whole MK grid unit totally inadequate for a ring final using 2.5 solid conductors. Admittedly the links could have been stranded 2.5 but nevertheless.
 
The cpcs are not the problem I did as suggested in #6 by @Strima just chopped the lot and put in a Wago with a link to the grid. The whole lot were so badly connected.
 

Reply to 6 cables in a backbox? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone... There are a total of 4 cables entering the junction box at the top of the staircase. Two 12/2 cables are coming in through the...
Replies
1
Views
458
Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units)...
Replies
1
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
518
Hello. Is it allowed to turn a 1.3" (34mm) thick 4-core (neutral and 3 phase) cable that is 7" (18cm) long, including outer insulation, at the...
Replies
8
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock