Here’s something I’ve never thought about until now….

So, we use the adiabatic to return an S based on the usual parameters and for arguments sake we end up with a 35mm conductor. But what if it’s also 300m+ length end to end before the earthing conductor gets to the MET? Do we then also calculate for vd, and if so based on what current (pefc?).
 
Not sure I've 100% understood the question but here are my thoughts/assumptions anyway:

The current that would flow under fault would be based on the impedance of the entire fault loop, so it would be the voltage across that entire loop (ie the supply voltage) that would be used to calculate it.

A longer circuit would mean higher loop impedance, and for some devices (fuses rather than MCBs) this would mean a thicker CPC is needed (I2t increasing as fault current decreases, so adiabatic calculation is made at the far end of the circuit). In these cases you'd need to calculate the adiabatic several times, for various thickness CPC and the corresponding loop impedance.

Or have I totally misunderstood the question?
 
VD under fault conditions is irrelevant. As long as the csa calculated using adabatic equation is adequate to carry the fault current for the duration it will be ok.
If calculated its likely to be much higher than the tabulated VD but only for a split second or time it takes fault to clear! but as supply will be interrupted in any case, trying maintaining a VD of x% to supply equipment is pointless.
 
In designing the cable size there are, as we all know, these key requirements:
  • Current carrying capacity suitable for max load (fixed) or OCPD (sockets, etc)
  • Fault impedance L-E Zs low enough to achieve disconnection times (from high enough PFC)
  • Supply impedance L-N low enough to meet load VD
  • Conductors able to survive the adiabatic heating during fault clearance
They are all interrelated of course but usually I would start with CCC for the minimum size for a short cable, and then VD to get any size increase, then check if Zs & adiabatic is met and possibly increase again (or size CPC up to live). To specifically answer your question, the answer is almost certainly "yes" that you need to iterate through the calculations again, just as @Pretty Mouth said since failing on VD might mean your Zs is too high to meet disconnection times and I2t of the OCPD could be far higher than the usual assumptions.

Meeting 5% VD overall implies a PSCC of 20x operating rating, that is usually enough for the OCPD disconnection. But that 5% spec is on the circuit and not necessarily including the supply impedance (though if it is a small load off the CU then it probably is close enough), and also meeting VD is based on L & N sizes, not L & E as E is often smaller (hence the adiabatic calculation) or higher Z (if SWA armour used).

Tables B1-B5 in the OSG are handy cheat-sheets for this when dealing with fuses, they give you the Zs requirements for a given CPC size so are solving both disconnection time (TN systems) & adiabatic for you.
 
Last edited:
Just to add that disconnection on the RCD rather than OCPD might meet time for safe ADS, but you have to allow that the 't' in your I2t could be 40ms for instant RCDs or much more for any delay versions. Depending on the PFC you might not meet the adiabatic as you would normally expect for MCB disconnection on the magnetic trip which is way faster.
 
Thanks all, between you you've clarified my thoughts as to what I need to do in this particular case - GN8 wasn't much help!! This application is where there are multiple separate generating sets working in tandem with a 2000A DNO source (not adding into it, obviously!) but distributing across a common earthing zone, so everything needs tieing back to the MET in a sort of Multiple Main Earth / Bonding mash-up where nothing is a short walk.
 
If it is the TN-C-S bond size for extraneous conductive systems then length is not really an issue, as the size is more down to the long-term open PEN current that might be seen, but for a 2000A supply I would imagine it is a local transformer so not that case? That would be a bit outside of Table 54.8 range!
 
If it is the TN-C-S bond size for extraneous conductive systems then length is not really an issue, as the size is more down to the long-term open PEN current that might be seen, but for a 2000A supply I would imagine it is a local transformer so not that case? That would be a bit outside of Table 54.8 range!
Yeah, hence my post! I'll temporarily have a 2000/3A DNO source, a 500kVA setup, a 300kVA setup and a baby 160kVA all working separately but needing bonding/earthing as it's the same location and a sh*t tonne of common structural steel, concrete and steel railings designed to be touched with temporary power and signal looms running randomly all over the place! Theoretically, a momentary fault on the DNO PEN would imply that all the interconnections might be required to carry the entire fault current (although Kirschoff applies and we're talking milliseconds before the sets would all go into protect mode anyway having upset the software).
 

Reply to Calculation of VD within/as well the adiabatic? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
803
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
448
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
My brain has been exercised a bit by this. Am I on the right lines with this extremely simplified example: If we take: -TNCS installation with a...
Replies
11
Views
4K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock