Discuss Floodlights and SWA cable. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
25
Hi all.
I have been asked to put two lights on two 30ft floodlight pylons. (one on each)
They need to be at around 6-8ft high. It will be a new circuit and run in SWA.
Is it 'correct' or acceptable to run the cable up the pylon to that height? (on the outside)
Also, any ideas on cable fixings for the above? Or, would an alternative way of doing this job be better?

Many thanks in advance.

Gerry.
 
Have done this before we fixed a 200x200 wooden plate to the pole and mounted our light and adaptable box (with a stuffing gland for the light flex) to this then cleated the armoureds down the pole, looked quite nice just make sure you make the plate to suit your fitting
 

Reply to Floodlights and SWA cable. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
Hi all, I am planning to install wall lights such as these ones (LAP Bronx Outdoor Up & Down Wall Light Black - Screwfix -...
Replies
5
Views
670
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
426
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Just received a Eufy CCTV floodlight camera (This one) which requires existing wiring. We have two outdoor lights on the side of our house with a...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock