Discuss Is a 35mm cable big enough for a 3-phase domestic installation with... in the UK Electrical Forum area at ElectriciansForums.net

they're planning on putting in a 35mm cable

Who is the 'they' in this case? The DNO or your electrical contractor?
If it's the DNO, what cable they use is out of your control. They will size their equipment according to their regulations and specs, to meet your agreed requirements which should have been calculated by the electrician before the application was made. The methods they use to size cables are different to the ones electricians use within an installation, as they have different performance specifications to meet under the ESQCR, for example.

If it is your electrician installing the said 35mm², then they should be able to calculate the cable to meet the requirements of BS7671 for whatever you have asked them to install either now or in the future. The worst case will be all demand or all generation - i.e. the maximum power that can flow in either direction. From what you have stated, the demand will significantly outweigh the generation, but is likely to be within 69kVA.

As mentioned above there are many factors built into the cable calculations, not just the load. Without all the information from a site survey, it's difficult to give a definitive answer to whether a particular cable size is suitable. 35mm² is in the right ballpark.
 
Who is the 'they' in this case? The DNO or your electrical contractor?
If it's the DNO, what cable they use is out of your control. They will size their equipment according to their regulations and specs, to meet your agreed requirements which should have been calculated by the electrician before the application was made. The methods they use to size cables are different to the ones electricians use within an installation, as they have different performance specifications to meet under the ESQCR, for example.

If it is your electrician installing the said 35mm², then they should be able to calculate the cable to meet the requirements of BS7671 for whatever you have asked them to install either now or in the future. The worst case will be all demand or all generation - i.e. the maximum power that can flow in either direction. From what you have stated, the demand will significantly outweigh the generation, but is likely to be within 69kVA.

As mentioned above there are many factors built into the cable calculations, not just the load. Without all the information from a site survey, it's difficult to give a definitive answer to whether a particular cable size is suitable. 35mm² is in the right ballpark.
The 'they' is the DNO, National Grid who are doing the install. The cable in the street coming to my property is 95mm according to the DNO engineer. That's about as much as I know.
Thanks for the advice.
 
It's not the size of the cable you yourself need to worry about. You need to tell them how many amps/kva you require and then let them worry about what size cable they need to install to be able to safely provide you with that.

If you have a 3phase 80amp supply and they install a 35mm cable, you'll be able to use 3phase 80amps. If they install a 70mm cable, you'll still only be able to use 3phase 80amps.
 
What the DNO can give you depends on many factors, not just the cable to your property. For example, the local substation might be close to max capacity based on all other property's loads in which case they might not offer new connections, or if they do it might not be 100A but instead fused down to 80A or 63A protect their system from overload.
 

Reply to Is a 35mm cable big enough for a 3-phase domestic installation with... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Help please, this is my first post on this subject regarding solar panel / battery installation into house with 3 phase supply. I am a DIY level...
Replies
0
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
502
Hello folks. I am about to complete on a (detached) house purchase and I want to ask your advice whether to have three phase connected to the...
Replies
24
Views
2K
Hi all, I have a regular client who has asked for a battery back up system to be installed at their home. They live in a rural location on a...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock