Discuss Testing PV Install in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

M

Mark Davey

As i'm fairly newto the PV market I wonder if anybody can confirm whether or not it is acceptable to use the information obtained from the inverter for the required test results? rather than phisically conducting the test?
 
The test results you need/want are Voc and Isc, which the inverter won't measure for you, it can only measure Vmp and Imp.

It also won't do the insulation test for you!

Pretty much that ^ I can sometimes be testing 20 a day and it doesnt really take that much longer to do it properly, just a few screws. If your trying to save time doing the testing make up a DC testing box with flying lead poking out.
 
Hi. Might it be a good idea for one of you experienced installers to make a test and inspection video to help all the new guys to do the job to a high standard, hope that dos`nt sound patronising, i`m the head of sales so i dont get to see any testing either.
 

Reply to Testing PV Install in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
446
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
969
Hi,first off this does not relate to work I intend to DIY. I'm trying to sanity check information I've been asked to provide to the installers. I...
Replies
0
Views
796
G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
610

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock