Most of have 10mm and 16 mm to hand .... 10 mm nearly every time for me
Discuss Understanding minimum CPC requirements? in the UK Electrical Forum area at ElectriciansForums.net
Yes that is correct.
The CSA of the earthing conductor with both TN-S and TT can be less than that of the bonding conductors.
There was one edition of the OSG which said the minimum CSA for the earth in TN-C-S was 6mm2.Yup - shame the muppets who are assessing people don't seem to understand this
I blame the pretty pictures in the front of the OSG