Discuss Multiple lights went out at same time. Supply issue? in the UK Electrical Forum area at ElectriciansForums.net

bubba0019

DIY
Reaction score
0
I have had no issues until this week. The lighting in my basement all has gone out. This includes my laundry room, basement game room, and the bathroom. I thought that it was just a blown fuse but no fuses were tripped. I checked switches and bulbs and ruled those out. I still have power in electrical outlets throughout those rooms. I have searched for GFI's but I have not found any that are tripped unless there is one hidden somewhere that I don't know about. I read about using multimeters and I have one but not really any skill in using it. It seems to be a supply issue. I remoted the switch plate covers and switches. All connections looked good. I switched all the breakers on and off. I did hear a mouse in my walls the other night. Maybe zapped? I recently replaced a ceiling fan in my dining room with a traditional light but all has been working fine for over a week. Also the wire to the dining room was the end of the run with only two wires.

Advice is appreciated.
 
The question is whether all those points are on one circuit? If so, it could still be just a broken connection in the last working point along the circuit rather than any of the dead ones. Of course it could equally be in a hidden junction box but let's hope not.

If it is a supply problem, then all circuits on that leg would be affected and most likely around half of all outlets and lights, and any 240V equipment like A/C would be dead.
 
I have had no issues until this week. The lighting in my basement all has gone out. This includes my laundry room, basement game room, and the bathroom. I thought that it was just a blown fuse but no fuses were tripped. I checked switches and bulbs and ruled those out. I still have power in electrical outlets throughout those rooms. I have searched for GFI's but I have not found any that are tripped unless there is one hidden somewhere that I don't know about. I read about using multimeters and I have one but not really any skill in using it. It seems to be a supply issue. I remoted the switch plate covers and switches. All connections looked good. I switched all the breakers on and off. I did hear a mouse in my walls the other night. Maybe zapped? I recently replaced a ceiling fan in my dining room with a traditional light but all has been working fine for over a week. Also the wire to the dining room was the end of the run with only two wires.

Advice is appreciated.
Since you are having issues in your laundry room and assuming your dryer is 240vac then you probably need to hire an electrician. You mentioned mice in your walls possibly chewing on wiring and can get in panels. You must have a Edison base fuse box which are outdated and the cover needs to come off to inspect it. Please hire an electrician
 

Reply to Multiple lights went out at same time. Supply issue? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I just found this forum last night and figured I would post my issue since I can't find much out there with a similar situation. My job...
Replies
4
Views
412
Hello, I added a 240v insta hot water heater at the kitchen sink. When the water heater is in use the lights in the adjacent dining room flicker...
Replies
1
Views
759
Hi all, I'm wondering if anyone might be able to help. We have a fused switch that controls 4 LED lights next to a power socket which have both...
Replies
11
Views
1K
Recently moved into a house from the 70s. There's no ceiling light in the living room. Assuming the switch for the room was to one of the outlets...
Replies
1
Views
435
Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
466

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock