Discuss Niceic Assesment in the UK Electrical Forum area at ElectriciansForums.net

I see I completely mis-remembered and the IR was 18Mohms. Unless you have time on your hands I'd leave that.
The main thing with this (and other comments) was you having a comment ready for an assessor picking it up. I've known assessors not give an IEC a 2nd glance, and a different one spent 30 minutes talking about it! Luck of the draw really....
 
I see I completely mis-remembered and the IR was 18Mohms. Unless you have time on your hands I'd leave that.
The main thing with this (and other comments) was you having a comment ready for an assessor picking it up. I've known assessors not give an IEC a 2nd glance, and a different one spent 30 minutes talking about it! Luck of the draw really....
I had an email from assessor to email him IEC. Please advise if it is good enough to emailed to him. Could you please information why insulation reader is lesser when testing between Live-Earth than live- live?Thanks
 
I had an email from assessor to email him IEC. Please advise if it is good enough to emailed to him. Could you please information why insulation reader is lesser when testing between Live-Earth than live- live?Thanks

Looks ok.. My only comments and they are very minor.

1. Under main switch, put N/A in all empty boxes so it cannot be modified..
2. In your insulation resistance tests you have a variety of greater than values, generally you put greater than when you reach the limit of your tester, think some older MFT were 299, hence you will often see >299, if its a modern one that goes upto 999 then put the reading you have not >200 as its a record that will help future electricians so being more accurate is better.
3. Under test instruments details, I would put the make and model of the MFT not just "MFT"
4. This is an EIC not EICR so you should not have general limitations, but if there are circuits where you cannot do testing say Live to neutral insulation resistance, then these circuits and reasons should be stated in details of circuits vulnerable to damage when testing. You should really be doing L-N on an EIC unless it is not feasible, and if it is not feasible then write why. The only circuit you identified is smokes although thats the only circuit you have actually fully tested so why is it identified as a circuit that could be damaged by testing? Sockets you should unplug everything and isolate any FCU's, if they have multiple usb sockets or there are sockets with things plugged in that you cannot reach without moving heavy furniture risking damage then thats fair enough but put that. Again with lighting you should remove all lamps and do L-N testing, if they have a load of downlights with integrated LED's then again fair enough its not feasible to disconnect them but put that.

Not doing L-N insulation resistance testing he might pick you up on it as it stands out that you have not put reasons for not doing it and looks like you have just avoided it which is fine if its a limitation on an EICR but not for an EIC.
 
The test instrument/s are identified by serial number. For an existing installation and consumer unit replacement there is no way an assessor would question omitting line to neutral insulation resistance testing, they are existing circuits so the test is irrelevant. Writing twaddle like sensitive equipment etc.... is too much information it is not important.
 
The test instrument/s are identified by serial number. For an existing installation and consumer unit replacement there is no way an assessor would question omitting line to neutral insulation resistance testing, they are existing circuits so the test is irrelevant. Writing twaddle like sensitive equipment etc.... is too much information it is not important.

Well that is what I got taught by multiple instructors and tutors. an EICR you can put whatever limitations you want as long as you list them, you can omit entire circuits if you want, say you were doing an EICR for a flooded house, presuming the cu was well above the flood level, there is no point needing to test the upstairs sockets or lighting...

An EIC I was always taught should not have any limitations, although in the real world I agree its not always practicable, my point was putting LIM on all L-N makes it look like he just cant be bothered to do it or is testing like an EICR, where do you stop, LIM on L-CPC just incase. Cant be bothered to do R1+R2, might as well LIM that, and Zs cause you LIM R1+R2 would have to be done live, so might as well LIM that as well..

Different electricians fill out the forms differently and different electricians believe what they do is correct but think about it, in EICR's there is a part for limitations, this is not in an EIC. If limitations were allowed why would you not have the same part that is in an EICR to write limitations in an EIC?

Different assessors focus on different things. Mine last picked me up on not having fire rated clips on my conduit... In a plastic shed... When I pointed this out he was like "Oh um yeah well obviously here its ok but I meant just in general dont forget them."
 
I'd agree, it now looks fine. I'd missed the variety of > IR readings first time.
I think it's fair enough that you didn't to L->N tests on the existing circuits for a CU change, it's fair enough to note smoke alarms as sensitive (i.e. heads need removing before L-N IR tests in future) and it's good you fully tested the new circuit.
(I would generally agree that avoiding LIM's on an EIC is a good principle to aim for)
But yes, that is a good certificate and could be sent.

Could you please information why insulation reader is lesser when testing between Live-Earth than live- live?
Sorry, I don't have an answer for that. I'd be content the readings exceed GN3 pass values if I were you.
All the best for your assessment.
 
Last edited:
Well that is what I got taught by multiple instructors and tutors. an EICR you can put whatever limitations you want as long as you list them, you can omit entire circuits if you want, say you were doing an EICR for a flooded house, presuming the cu was well above the flood level, there is no point needing to test the upstairs sockets or lighting...

An EIC I was always taught should not have any limitations, although in the real world I agree its not always practicable, my point was putting LIM on all L-N makes it look like he just cant be bothered to do it or is testing like an EICR, where do you stop, LIM on L-CPC just incase. Cant be bothered to do R1+R2, might as well LIM that, and Zs cause you LIM R1+R2 would have to be done live, so might as well LIM that as well..

Different electricians fill out the forms differently and different electricians believe what they do is correct but think about it, in EICR's there is a part for limitations, this is not in an EIC. If limitations were allowed why would you not have the same part that is in an EICR to write limitations in an EIC?

Different assessors focus on different things. Mine last picked me up on not having fire rated clips on my conduit... In a plastic shed... When I pointed this out he was like "Oh um yeah well obviously here its ok but I meant just in general dont forget them."
Yes I agree the EIC should not show Limitations I did not really view it. I just leave them blank no assessor is going to care for an existing installation.
 
Well that is what I got taught by multiple instructors and tutors. an EICR you can put whatever limitations you want as long as you list them, you can omit entire circuits if you want, say you were doing an EICR for a flooded house, presuming the cu was well above the flood level, there is no point needing to test the upstairs sockets or lighting...

An EIC I was always taught should not have any limitations, although in the real world I agree its not always practicable, my point was putting LIM on all L-N makes it look like he just cant be bothered to do it or is testing like an EICR, where do you stop, LIM on L-CPC just incase. Cant be bothered to do R1+R2, might as well LIM that, and Zs cause you LIM R1+R2 would have to be done live, so might as well LIM that as well..

Different electricians fill out the forms differently and different electricians believe what they do is correct but think about it, in EICR's there is a part for limitations, this is not in an EIC. If limitations were allowed why would you not have the same part that is in an EICR to write limitations in an EIC?

Different assessors focus on different things. Mine last picked me up on not having fire rated clips on my conduit... In a plastic shed... When I pointed this out he was like "Oh um yeah well obviously here its ok but I meant just in general dont forget them."
Thanks for your valueable comments. In my humble opinion this is not new installation.I changed the consumer unit and installed a new circuit for smoke alarm .I mentioned this under
"Extent of the installation covered by this Certificate". Please correct me if I am wrong here.Thanks again.
 

Reply to Niceic Assesment in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
401
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
I'm about to order this wired smoke alarm system as it can network but I just went to see how my existing fire alarms are hooked up and there...
Replies
12
Views
1K
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
346
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
537

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock