Hi there,
I was just looking to find out what would be the most appropriate reference method to use.
the distribution circuits leave the fuse board in 3 meters of trunking, then onto basket most of the ciruicts at lower lever then come down the wall in conduit which has been pre installed in pods. And the kitchen we have installed steel conduit.
Sorry to sound silly I have read the reference methods and was inclined to say B.

Many thanks in advance

LH
 
^^ What he said. (Hopes no-one sneaks in a silly post after Leesparkykent before I hit "reply")

If any of the conduit/trunking is in thermal insulation then "A", otherwise it looks like "B", as you've said.
 

Reply to Reference Methods?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys Is there a reason why installation ref method B (in conduit or trunking on a wall) not listed as an allowed installation method on the...
Replies
3
Views
831
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hey all, Excuse the ignorance here but I wonder if you lovely folk might have any opinions or better still be able to point in the right direction...
Replies
20
Views
7K
A
I am trying to select a suitable conductor size from Fig 4D1A of the BS 7671 Book, and am encountering a problem because the circuit does not...
Replies
6
Views
12K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock