Discuss Swa 4core cable used as two 2core circuits in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
101
Working on a job have found a 4core cable going into a weather proof box and splitting up into 2 circuits again at the board it split in two single phase MCB s . My question is would you judge the current carring capacity of the cable as a two wire or four wire
 
Working on a job have found a 4core cable going into a weather proof box and splitting up into 2 circuits again at the board it split in two single phase MCB s . My question is would you judge the current carring capacity of the cable as a two wire or four wire
What is your opinion on the subject, also taking into consideration the size of the cpc and any bonding that may be required?
 
it's OK, they been busy on the church roofs while the weather is fine. saving cable nicking for a rainy day.
 
I always consider the three phase ccc, same for a three core cable as a single phase supply with one core used for a cpc. I think the Tables in 7671 should be reconsidered as they only consider two core for single phase and three or four core to be three phase. Ccc for YY, CY and SY apply correction factors for core quantity as opposed to the number of phases and I think think this is more informative.
 
I did a job feeding two portacabins about six months ago and used two 3 core cable two feed them and it got me thinking when I seen this today as the two feeds had to be run though ducting and both had to be put in weather proof box es to be connected to flex to be plugged in to the portacabins and I thought it would of been cheaper and quicker to do this if I had a similar job in the future
 
it's OK, they been busy on the church roofs while the weather is fine. saving cable nicking for a rainy day.
Thieving so and sos. still it comes natural to a dyed in the wood Scouser, part of the curriculum at the last stages of the 4th year at secondary School.
 
Thieving so and sos. still it comes natural to a dyed in the wood Scouser, part of the curriculum at the last stages of the 4th year at secondary school Borstal .
corrected that for you.
 
Well it is related to something else that happen lately all my large swa off cuts have been robbed and a 35 meter lengtt of 50mm 4core which I cut out off the ceiling cos it had been damaged has went as well . That was my graft and some pr#£k has robbed it before I could
 
I did a job feeding two portacabins about six months ago and used two 3 core cable two feed them and it got me thinking when I seen this today as the two feeds had to be run though ducting and both had to be put in weather proof box es to be connected to flex to be plugged in to the portacabins and I thought it would of been cheaper and quicker to do this if I had a similar job in the future
No reason why you cannot do this providing the armour is effective for earthing purposes, the drawback is if it is required to support main protective bonding where the minimum size to support 10mm bonding would be a 50mm 4 core cable.
 
I always consider the three phase ccc, same for a three core cable as a single phase supply with one core used for a cpc. I think the Tables in 7671 should be reconsidered as they only consider two core for single phase and three or four core to be three phase. Ccc for YY, CY and SY apply correction factors for core quantity as opposed to the number of phases and I think think this is more informative.
I know it's not "right", but I'm thinking 2.3.3.1 which would give a Cg of 0.5 here (?).
 

Reply to Swa 4core cable used as two 2core circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
633
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
774
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
475

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock