Every circuit has the potential to be extremely dangerous if it is not installed and tested properly, why would you single out ring circuits for this?
How old are the circuits you are finding these issues with? Are they reasonably modern circuits which have been fully tested at the time of installation or are they older circuits which may not have been tested at install or have been fiddled with over time?
And 4mm radials are far more limited, fart near the cable and the CCC drops below 32A.
All sorts, new colours through to late 1970's stuff.
Yes they will have been modified poorly but that's my point, at least an overloaded radial (As long as the MCB isn't over-rated) will just trip rather than work fine up until the point the smoke starts.
I mean unless clipped direct, you can't run it on a 32A mcb.Is there a CCC chart for 2x2.5mm T&E?
Or do you mean the 100 square metre area allowed of a ring circuit?
How many ring circuits have you encountered with broken continuity that have been overloaded to the point where the smoke starts ?
I mean unless clipped direct, you can't run it on a 32A mcb.
Me too. I fully support and endorse the ring final circuit when used appropriately and correctly.I like them.
Precisely.Isn't that the fault of the people who tinker with the circuits without knowing what they are doing. Maybe they should ban them instead.
I wouldn't know about that, but I do know that my commercial customers have ring circuits installed for the output of static inverters and central battery systems to reduce voltage drop and give redundancy, especially on lower voltage DC circuits.
Car park lighting or large area lighting also utilises ring circuits to limit volt drop and cable size.
Distribution circuits, both LV and HV, utilise various forms of ring circuits, mostly for redundancy.
You would sure as hell see a lot more power cuts if a universal ban on ring circuits was applied across the country
Ring final circuits are here to stay like them or not what I really love when testing them are the people who save ÂŁ5 a year but putting two cpcs through one sleeve, maybe even twisting them together at the same time.
That's my favourite type of ring circuit.OK fine. For the sake of clarity/pedantry I was referring to a 32A ring final circuit, with 2.5mm live conductors and a 1.5mm CPC, in a domestic/unsupervised situation.
Ring final circuits are here to stay like them or not what I really love when testing them are the people who save ÂŁ5 a year but putting two cpcs through one sleeve, maybe even twisting them together at the same time.
Found an immersion heater on a ring this week with only 2 other bedroom sockets on it . The load was 3kw for the heater and all tests are good so as it was an old install and it was an CU change only . Rings Rule !!!!!!!!!!!!!!! . PS Did reduce the rcbo to 20 amps
Reply to Why aren't ring circuits banned? in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.