Discuss Why aren't ring circuits banned? in the UK Electrical Forum area at ElectriciansForums.net

Every circuit has the potential to be extremely dangerous if it is not installed and tested properly, why would you single out ring circuits for this?

How old are the circuits you are finding these issues with? Are they reasonably modern circuits which have been fully tested at the time of installation or are they older circuits which may not have been tested at install or have been fiddled with over time?

All sorts, new colours through to late 1970's stuff.

Yes they will have been modified poorly but that's my point, at least an overloaded radial (As long as the MCB isn't over-rated) will just trip rather than work fine up until the point the smoke starts.
 
All sorts, new colours through to late 1970's stuff.

Yes they will have been modified poorly but that's my point, at least an overloaded radial (As long as the MCB isn't over-rated) will just trip rather than work fine up until the point the smoke starts.

How many ring circuits have you encountered with broken continuity that have been overloaded to the point where the smoke starts ?
 
How many ring circuits have you encountered with broken continuity that have been overloaded to the point where the smoke starts ?

One today that's why I posted.

I guess I'm just amazed that something that has the potential to cause serious damage is just fine, while we're now told to C3 plastic consumer units and make sure there's RCD protection for near enough everything.

Oh well, clearly in a minority of 1. :D
 
I wouldn't know about that, but I do know that my commercial customers have ring circuits installed for the output of static inverters and central battery systems to reduce voltage drop and give redundancy, especially on lower voltage DC circuits.
Car park lighting or large area lighting also utilises ring circuits to limit volt drop and cable size.
Distribution circuits, both LV and HV, utilise various forms of ring circuits, mostly for redundancy.

You would sure as hell see a lot more power cuts if a universal ban on ring circuits was applied across the country

OK fine. For the sake of clarity/pedantry I was referring to a 32A ring final circuit, with 2.5mm live conductors and a 1.5mm CPC, in a domestic/unsupervised situation.
 
Found an immersion heater on a ring this week with only 2 other bedroom sockets on it . The load was 3kw for the heater and all tests are good so as it was an old install and it was an CU change only . Rings Rule !!!!!!!!!!!!!!! . PS Did reduce the rcbo to 20 amps
 
Found an immersion heater on a ring this week with only 2 other bedroom sockets on it . The load was 3kw for the heater and all tests are good so as it was an old install and it was an CU change only . Rings Rule !!!!!!!!!!!!!!! . PS Did reduce the rcbo to 20 amps

What's wrong with an immersion heater on a ring? It's been pretty common for decades. I wouldn't do it on a new installation, but see no issue with it as an alteration to an existing install.
Why reduce the size of the ocpd? Was there something wrong with the circuit?
 
Immersions on rings should be less of an issue nowadays. With modern Central heating people us a lot less electric heaters so ring loading is often less than it would have been when elec was cheap.
 

Reply to Why aren't ring circuits banned? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
859
Afternoon all, A quick EICR question. I have found a Ring Final Circuit that has been run in 1.5/1mm twin and earth. It is RCD protected and OCPD...
Replies
24
Views
4K
Hello everyone, I know this has come upquite often, I have gone back through the many threads relating tothis topic. The reason for wanting to...
Replies
26
Views
15K
GEOFF S
G
Hi all I got called out to a fault yesterday and thought I'll share with you how I discovered the fault I received a phone call and the customer...
Replies
3
Views
1K
Eh up :) I don't do EICRs - not enough experience - but the things I see on some reports done by others really dismay me. Perhaps some of my...
Replies
21
Views
5K
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock