As has been mentioned, if the CU is more than 3m away, it's almost certain that the DNO will require additional fusing.
i would go with individual fuses per CU, and mount the whole lot on steel trunking. It's cheap, easy to use and won't take long.
Make sure the locknuts are tight. I would fly lead from the trunking to each individual switch fuse.
will the armour on the 16mm 2 core be upto the spec for the bonding if its TNC-S? suspect not, but I'm not aware of all the facts as you are.
Don't forget that for main bonding of PME supplies, it's the conductivity that is of prime concern, unlike the adiabatic, in which limiting temperature is the concern.
i would go with individual fuses per CU, and mount the whole lot on steel trunking. It's cheap, easy to use and won't take long.
Make sure the locknuts are tight. I would fly lead from the trunking to each individual switch fuse.
will the armour on the 16mm 2 core be upto the spec for the bonding if its TNC-S? suspect not, but I'm not aware of all the facts as you are.
Don't forget that for main bonding of PME supplies, it's the conductivity that is of prime concern, unlike the adiabatic, in which limiting temperature is the concern.