As has been mentioned, if the CU is more than 3m away, it's almost certain that the DNO will require additional fusing.
i would go with individual fuses per CU, and mount the whole lot on steel trunking. It's cheap, easy to use and won't take long.
Make sure the locknuts are tight. I would fly lead from the trunking to each individual switch fuse.
will the armour on the 16mm 2 core be upto the spec for the bonding if its TNC-S? suspect not, but I'm not aware of all the facts as you are.
Don't forget that for main bonding of PME supplies, it's the conductivity that is of prime concern, unlike the adiabatic, in which limiting temperature is the concern.
 
As has been mentioned, if the CU is more than 3m away, it's almost certain that the DNO will require additional fusing.
i would go with individual fuses per CU, and mount the whole lot on steel trunking. It's cheap, easy to use and won't take long.
Make sure the locknuts are tight. I would fly lead from the trunking to each individual switch fuse.
will the armour on the 16mm 2 core be upto the spec for the bonding if its TNC-S? suspect not, but I'm not aware of all the facts as you are.
Don't forget that for main bonding of PME supplies, it's the conductivity that is of prime concern, unlike the adiabatic, in which limiting temperature is the concern.

Well spotted, yes all the CU's are more than 3M away. I was just driving back and thought I should mention this, but you beat me to it. This is one reason for using the Wylex Rec Isolators. I assume they are okay for the job?

Also worth mentioning is I also chose these for size as we don't have a lot of room in the intake cupbord.
 
Last edited:
Well spotted, yes all the CU's are more than 3M away. I was just driving back and thought I should mention this, but you beat me to it. This is one reason for using the Wylex Rec Isolators. I assume they are okay for the job?

Also worth mentioning is I also chose these for size as we don't have a lot of room in the intake cupbord.

The Wylex REC isolators aren't fused; so not OK.
 
If you have 12 number of flat's to supply, you maybe better off thinking about a Ryefield panel at the intake cupboard Where all the fuses are located in the one panel.

What do you have there, a 3 phase DNO supply??
 
Unless I've completely misunderstood all this, this sounds like a classic case of over engineering through misunderstanding. What's wrong here with Intake > KMF > 16mm TE plus additional 10mm cpc if the adiabatic is over 6mm? Easy to run, easy to terminate and much cheaper plus adding a fuse into the system.
 
Unless I've completely misunderstood all this, this sounds like a classic case of over engineering through misunderstanding. What's wrong here with Intake > KMF > 16mm TE plus additional 10mm cpc if the adiabatic is over 6mm? Easy to run, easy to terminate and much cheaper plus adding a fuse into the system.

If they are flats then the chances are the subs would need RCD protection if ran in T&e
 
What is you’re objection to trunking? If there are 12 cables to make off I can’t think of a better option. 12 X adaptable boxes are going to look a mess.
As for the CPC E54’s table shows that you are right to use the armouring.
 

Reply to Terminating SWA with Wylex REC Supply Isolators in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
882
I haven't seen a lot of discussion on this subject and have questions pertaining to isolation where TN earthing is present and any peculiarites...
Replies
21
Views
654
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
749
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock