Discuss Need some ideas - RCD tripping but everything tests fine.... in the UK Electrical Forum area at ElectriciansForums.net

You are right Bigspark, it is a pants installation at the moment, I will recommend this but she is on a budget, so 5 RCBOs and a Type S main switch (plus labour) is most likely not going to go down well.... I'll see what she says.
So far the 'swapped' RCCB hasn't gone again, but I am not holding out great hopes!
Cheers for the advice & opinions everyone.

The price won't go down well, but how much food is in her freezer..... This would go to waste if it trips and she's not around......
 
You are right Bigspark, it is a pants installation at the moment, I will recommend this but she is on a budget, so 5 RCBOs and a Type S main switch (plus labour) is most likely not going to go down well.... I'll see what she says.
So far the 'swapped' RCCB hasn't gone again, but I am not holding out great hopes!
Cheers for the advice & opinions everyone.
Do you mean a type S 100mA RCD as the main switch?
 
hi weevilward
had a similar issue turned out to be a wine fridge some years ago, TT system everything on one RCD unit. would not be so bad if it was not in the cellar, every time we tested the circuit we unplugged the fridge to plug in lead light, found a problem on a ring short caused by a mouse, repaired tested time I got home phone call gone again, went back showed house keeper readings on meter IR testing circuit all clear.
anyway customer had all CB's replaced with RCBO units for each circuit & when it went again called me before turning on the RCBO, went in new wine fridge 3 months old causing issue. Maytag replaced no questions asked, did not help client with approximately 4 days of work caused by the fridge.
earth leakage meter very good used one of those a few times very helpful if you can turn on appliances whilst watching the readings.

have also had another fault about 10 years ago TT system same again 30ma trip on mains, IR tested whole house after I managed to take out all of the Neon indicated extension leads must have been 20-25 leads in the house, sh..t loads of electronics plugged in. spent all day on it IR tested could not locate, turned system on again plugged in & RCD down after 10-15 seconds, owner well it must be on a circuit I stripped down the conservatory, kitchen, lounge, heating, immersion, shower. each time I turned the system on I used hoover on each socket circuit & did not matter which one, owner did not believe me thought I was having him on that it was sheer over load of the RCD unit (30ma).
mentioned I would change board agreed price as I had already undertaken all of the testing on the whole house in that day & had results, agreed deduction on my days wages against fuse box change picked my money up next day got phone call my mate will change for less than you.
I lost it & called him c...t, told him good luck with testing his f.....king house, as I would not give him my notes as he did not want to pay for them.
Nasty customer, marc8, well avoided...
Thanks for th advice, I am going to invest in an earth leakage meter - any recommendations?
 
Or upfront before CU. I know this is a bone of contention on forums - some people say normal main switch and all 30mA RCBOs is fine, others prefer to fit time delay 100mA as well. Don't especially want to go off topic here....
Pretty sure crabteee starbreaker don't do a 100mA type S main switch so it'd have to be upfront before CU
 
Or upfront before CU. I know this is a bone of contention on forums - some people say normal main switch and all 30mA RCBOs is fine, others prefer to fit time delay 100mA as well. Don't especially want to go off topic here....
I would go for this as it offers double pole isolation whereas the rcbos do not.
 

Reply to Need some ideas - RCD tripping but everything tests fine.... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
844
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
917
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock